UTS10BI 240 volt power input

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI 240 volt power input
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
6
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

UTS10BI 240 volt power input

Hello,

I recently purchased the UTS10BI to work with a Honda EU6500i generator.


The generator has a 30 amp output receptacle, and another 120/240 volt receptacle.

The 30 amp output is 120 volts only.

My question is, can I power the UTS10BI on circuits 9 and 10 using the main

breaker panel off of utility power - and - have a UPS connected as default "backup2",

*without* inputting 240 volts from the generator ? - the idea is to get the maximum

30 amp capacity off the generator on that single receptacle (because the 120/240

volt receptacle is limited to 22 amps or so).

I would think this "should" work, since the UTS10BI powered up when I plugged

120 volts into the UPS input port. So my reasoning is, "if" I can power the UTS10BI

via the UPS, then I don't need to feed it 240 volts off the generator, and can use the

single 30 amp output for more capacity on circuits 1 to 8 on the UTS (vs. the other

reduced 120/240 one).


Or am I missing something regarding the operational logic of the box ?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

The UTS10BI and the Honda EU6500 work well together.  This is the setup I have. The UTS10BI is made to work off a 120/240V generator output.

The generator does not "feed" the UTS on circuits 9 & 10. It feeds the UTS through the generator input on the UTS. When on generator power, the odd circuits (1,3,5,7 & 9) are fed from L1 and the even circuits (2,4,6,8 & 10) are fed from L2. The EU6500 can provide about 22A on each phase, or 44A total. (It can supposedly be pushed even higher - see Guy Holt's excellent articles on this - Google search "Guy Holt EU6500is"). So the 120/240V outlet is the way to go if you have a generator so equipped (like the EU6500).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

Hi tom_b,

A 240vac input is required to power the UTS10BI at all times. Without the 240vac feed between circuits 9 and 10 while on Generator, the UTS10BI will never fully activate. In addition, the UPS Inlet is rated for 15amp and is limited in it's capability.

Given the type of generator you currently have, I would have recommended the UTS6H. The UTS6H is 120vac only and comes stock with an L30 receptacle.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

Hello,

Just to confirm, with the UTS10BI, feed it 240 volts (on circuits 9 and 10), and i'll

have 120 volts available on circuits 1-8 ? (albeit from the Honda it would be limited

to approximately 22 amps using the 120/240 output receptacle on it).

So if I understand the schematic correctly, it looks as if opposite phases are

assigned to odd/even outlets (ie. 1,3,5,7 on L1 and 2,4,6,8 on L2), I know this

has been asked before, but I'm not seeing *why* I cannot use 9, 10 in the

same manner (assign 9 to L1, 10 to L2). The neutral would have already been

connected at the main panel. So it would give me 120 volts at 9 and 10 but on

opposite phases.

Yes ? No ? Maybe ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

The UTS10BI and the Honda EU6500 work well together.  This is the setup I have. The UTS10BI is made to work off a 120/240V generator output.

The generator does not "feed" the UTS on circuits 9 & 10. It feeds the UTS through the generator input on the UTS. When on generator power, the odd circuits (1,3,5,7 & 9) are fed from L1 and the even circuits (2,4,6,8 & 10) are fed from L2. The EU6500 can provide about 22A on each phase, or 44A total. (It can supposedly be pushed even higher - see Guy Holt's excellent articles on this - Google search "Guy Holt EU6500is"). So the 120/240V outlet is the way to go if you have a generator so equipped (like the EU6500).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

Elec-Engr, thank you !

You gave me the missing piece that for some reason I wasn't

fully grasping (that I had 22 amps available on each phase to

get 44 amps total).


Awesome !

Thanks again smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

elec-engr,

Thank you for your input in this matter. Although I understand the inner workings of the UTS, I'm not too familiar with the full capabilities of the generator in question.

SecretSquirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:35 AM

The reason that you should NOT use outputs 9 and 10 as two separate 120 volt circuits is because the UTS10BI is designed for circuits 9 and 10 to be connected to a 240 volt load, and therefor, the current through both circuits should be virtually identical at all times. Under this condition, there would be no real benefit in measuring the current in both circuits, so the UTS10BI only measures the current in circuit 9 and assumes that the current in circuit 10 is the same for the purpose of power monitoring and overload protection calculations for the 240 volt load. This means if circuits 9 and 10 were to be used separately, their power monitoring and protection calculations would not be accurate, resulting in possible unreliable or unsafe conditions  Furthermore, circuit setup does not have provisions for setting the options for circuits 9 and 10 separately. In short, the UTS10BI will ALWAYS respond to circuits 9 and 10 as a pair, or in other words as a single load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of