APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Will either of these units work wired into a/powered by a 120V Inverter Generator (Yamaha ES2800i)? My generator does not output 240V, from the documentation and my understanding it's just not too clear if I can use either of these panels.
I just want to be able to use it to power 120V circuits I have in my house, right now I am pulling extensions cords all over the house when I need power during an outage.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Recently, One of my friend purchased the Yamaha EF2800i Inverter Generator 2800 Watt, It's Premium Consumer Generator, Rated AC Output 2500 watts, Fuel Tank Capacity 3.0 gallons, Continuous Operation at 1/4 Rated Load 12.9 hrs., Noise Level 60.0 - 67.0 dBA; Inverter system with Pulse Width Modulation (PWM) control; Multi pole alternator; Economy Control electrical governor; Cast iron cylinder lining; Oil Watch Warning System; DC Output 12 volt 8.3 amps and its features are " Economy Control" electrical governor- improves fuel economy and reduce noise level. Please produce produce some more attachments about the topic to view detail information.
generators
australia generators
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Looking further at the documentation it looks like the UTS6H is the 120V version.
Also - Looking at the wiring, I believe the 10 would work - however with that said, only half of the 120V circuits would work on either the left or right leg. (Excluding the 240V 9 & 10 as well) netting you only 4 circuits usable.
I am also not sure how the logic in the board would like this.. I'll either stick with the UTS6H 120V version, or pickup a 240V Inverter generator.
If you notice on the Honda site, they list the 2000i and 3000i genset's as being compatible with the 6H version, after that it goes up to the 240V versions..
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Gotcha.. Thanks.. Yeah I found the UTS6H at a few distributors. I may just pick one of those up for now and upgrade to the 10 when I upgrade my generator to something larger. Living in a townhouse, just can't go too large - nowhere to put it.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:38 PM . Last Modified: 2024-03-20 04:01 AM
Recently, One of my friend purchased the Yamaha EF2800i Inverter Generator 2800 Watt, It's Premium Consumer Generator, Rated AC Output 2500 watts, Fuel Tank Capacity 3.0 gallons, Continuous Operation at 1/4 Rated Load 12.9 hrs., Noise Level 60.0 - 67.0 dBA; Inverter system with Pulse Width Modulation (PWM) control; Multi pole alternator; Economy Control electrical governor; Cast iron cylinder lining; Oil Watch Warning System; DC Output 12 volt 8.3 amps and its features are " Economy Control" electrical governor- improves fuel economy and reduce noise level. Please produce produce some more attachments about the topic to view detail information.
generators
australia generators
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.