UPS x Surge Suppression Joule Rating.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS x Surge Suppression Joule Rating.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

0 Likes
2
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

UPS x Surge Suppression Joule Rating.

Why the surge suppression portion of all UPSses are almost always lower rated than those from a dedicated surge suppressor? See the exemple:

Backup-UPS RS BR1500

- Surge energy rating: 420 Joules

Backup-UPS ES BE650G:

- Surge energy rating 365 Joules

Even the bigger units from the Smart-UPS series and more professional ones have a lower surge ratings, why? Could it be that these units have a transformer inside and they would limit the surge peak? Some say transformers can do this, some say the surge "arresting" capability of a power transformers is very low, who is telling the truth?

Now the numbers from the APC SurgeArrest PF11VNT3:

Surge energy rating *2030 Joules*
EMI/RFI Noise rejection (100 kHz to 10 mHz) 70 dB
Peak Current Normal Mode 20 kAmps
Peak Current Common Mode 60 kAmps

BTW, why APC "hides" the peak current amps rating and the EMI/RFI noise rejection of the UPSses? Is there an specific reason for that? Why is it less important for the user to know this information when buying an UPS than when buying a dedicated surge protector, since UPSses can work as surge protectors as well?

I know the joule rating is not as important as Let Through Voltage and such, but that still doens't explain me the reason for the lower ratings for UPSses, since they're supposed to give your equipment more protection.

Thanks!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

Thanks for the tip, but I already have a whole house surge suppressor, one for each phase, but I think I should've put this question differently.

I've read something that says transformers acts a bit like surge suppressors I mean, they can theoretically reduce surges. I don't know how this statement is true, but I wanted to know if the presence of a transformer used for the voltage regulation could suppress part of the surge thus allowing the UPS surge suppressor componentes itself, MOVs and such, be smaller...

I still think APC should at least divulge the filtering numbers for their UPS units and the peak amps sustained by the UPS MOVs, that's not a hard thing to do since other brands do that! The MOV numbers are available on the MOV maker website and running some oscilloscope tests and also judging by the componentes used, capacitors, inductors... they can tell how much filtering the unit is capable of, as far as my scarce knowledge go.

I had to open my UPS to see what components were used. There is I think two "X" capacitors, one inductor coil, 4 "y" capacitors and or 4 or 5 10mm MOVs - I think they are 10mm... The specifications of them I can't recall right now...

Thanks once again!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

Rau,

While I understand completely what you're stating, you might want to look at the overall picture.

A UPS's primary feature is the battery back-up, not the surge protection.
A Surge Protector's primary feature is the surge protection.

If you are using a UPS system, and are worried about the surge protection, why not install a hardwired panelmount surge at the service entrance and not worry about anything being affected downstream? This would allow for EXCESSIVE surges/spikes to be harnessed by the panelmount, and IF it happens to go downstream, the UPS's surge surpression is capable of handling the rest.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:21 PM . Last Modified: ‎2024-03-26 12:32 AM

Thanks for the tip, but I already have a whole house surge suppressor, one for each phase, but I think I should've put this question differently.

I've read something that says transformers acts a bit like surge suppressors I mean, they can theoretically reduce surges. I don't know how this statement is true, but I wanted to know if the presence of a transformer used for the voltage regulation could suppress part of the surge thus allowing the UPS surge suppressor componentes itself, MOVs and such, be smaller...

I still think APC should at least divulge the filtering numbers for their UPS units and the peak amps sustained by the UPS MOVs, that's not a hard thing to do since other brands do that! The MOV numbers are available on the MOV maker website and running some oscilloscope tests and also judging by the componentes used, capacitors, inductors... they can tell how much filtering the unit is capable of, as far as my scarce knowledge go.

I had to open my UPS to see what components were used. There is I think two "X" capacitors, one inductor coil, 4 "y" capacitors and or 4 or 5 10mm MOVs - I think they are 10mm... The specifications of them I can't recall right now...

Thanks once again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore