UPS that measure load percent/watts while on line power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS that measure load percent/watts while on line power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
10
5024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

UPS that measure load percent/watts while on line power

Which series of UPS report load percent/watts while on line power? I think all Smart-UPS and Back-UPS Pro do report, at least some Back-UPS RS do also and Back-UPS ES do not. Please confirm and also what about CS, LS, VS, XS and Office?

Thanks,

Message was edited by: automate

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

OK, I found the following line in the PCPELog.txt, so the PowerChute developers must have a list of which UPS are considered "Advanced" and therefore there load value changes while on line power
"6/12/2011 7:38:14 AM :: HostApplication :: Start :: Information Message - Detected UPS type and the UPS connected is NOT an Advanced UPS. Data service will not poll for load changes."

Message was edited by: automate

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

well what i do know is back UPS ES, beginning with BE, is the lowest end UPS and RS, the highest end models, beginning with with BR are top end. thus, some features are supported and some not. another thing that BE models dont support is the run self test option that you see on the top left under Monitor System.

but, it is unorganized because I think something like the BE750G allows you to run a self test.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

how old is it? do you have the first few digits of the serial number on it? that is news to me so i guess we shouldn't go by what i am saying! is this what you are seeing via powerchute personal edition? i will check on this tomorrow with someone who will know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

they all should

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

Just to clarify, you are saying all models of all series except the ES should report load percent/watts while on line power (not battery)? Including discontinued models?

Message was edited by: automate

Message was edited by: automate

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

i am personally not aware of any APC UPS model that does not provide UPS load percentage while online AND on battery. the only one I am not 100% sure on is Back UPS office since it was before my time and I don't have one to look at. as far as I know, everything can detect and measure load no matter if it is running online or on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

I have an older Back-UPS 725 ES and it definitely does not measure load percent when it is on line power. The load percent that it responds with when on line power is the last value it measured the last time it was on battery power. It also uses this value to calculate how long that battery power will last if you loose power. So if you add or subtract load while on line power the estimated battery run time does not adjust.

Message was edited by: automate

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:59 AM . Last Modified: ‎2024-03-21 05:52 AM

Manufacture date 9/14/2004

Here is a quote from PCPE help file, page "Viewing basic power Information".
"Energy: This field display cycles between three different values, all relating to your energy usage for battery backup attachments. (For additional information, see Assessing your energy usage). *This information is not available for all battery backups*."

Here is a quote from the APCUPSD manual
[http://www.apcupsd.org/manual/manual.html]
"For the various smaller, cheaper APC USB UPSes, such as the CS, ES, ..., you will get much of the information that is presented above, but not all of it. For example, you will not get MAXLINEV, MINLINEV, LINEFREQ, ... and in particular, the LOADPCT will be zero when you are running on mains. LOADPCT will display when the UPS is on batteries. You must remember that the non-SmartUPSes are much simpler (and less expensive) and therefore produce less information."

Message was edited by: automate

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:52 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:52 AM

ok, sorry for the delay. i asked the tech support lead for Back UPS here at APC. he told me that all Back UPS are the same and should report data while online and on battery. granted, the data you receive while online is generally less accurate versus while on battery, but what I said is generally true. there should always be something reading in load percentage according to what we at APC think.

is this perhaps an apcupsd limitation?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

0 Likes
0
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

The BackUPS ES will send a loading value when it is on line-power but it does not change with actual load because it is from when the UPS was last on batteries. I checked another BackUPS ES and it is doing the same thing. It is Serial number JB0432016***. It is not an apcupsd issue. See the attached screen shots. Notice the BackUPS RS shows watts but the BackUP ES does not. This is because PCPE knows that the load percent/watt value is not correct from a ES when it is on line power

Message was edited by: automate

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

0 Likes
0
5022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:00 AM . Last Modified: ‎2024-03-21 05:51 AM

OK, I found the following line in the PCPELog.txt, so the PowerChute developers must have a list of which UPS are considered "Advanced" and therefore there load value changes while on line power
"6/12/2011 7:38:14 AM :: HostApplication :: Start :: Information Message - Detected UPS type and the UPS connected is NOT an Advanced UPS. Data service will not poll for load changes."

Message was edited by: automate

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore