Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS says no power via transformer?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS says no power via transformer?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Mavrck48
Mavrck48
Explorer

Posted: ‎2024-01-19 02:36 AM

0 Likes
3
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-19 02:36 AM

UPS says no power via transformer?

I just moved to Azerbaijan from the United States.  I brought my Pro 1500 S battery backup UPS with me.

 

Azerbaijan is 220v power, so I bought a voltage transformer to allow me to use my UPS.

 

So my setup is power outlet -> transformer -> UPS.

 

However, the UPS will not get off battery and is acting like there is no power.

 

Facts that I do know:

- The transformer is outputting power as I can plug other devices into it and they work.

- The wiring fault light is off on the UPS.

- I get the same results with two different UPS devices.

 

Am I missing something?  Is the transformer power output not correct or stable enough for the UPS?

 

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2024-01-19 07:06 AM

0 Likes
0
1967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-19 07:06 AM

In North America household power is 120 VAC 60 Hz. In Azerbaijan the power is 220 VAC 50 Hz. If the UPS had the ability and supported a wide voltage / frequency like they do for Enterprise models. The UPS would have auto detected the line voltage and frequency and operated just fine.

 

Given the model you have does not have that capability more than likely the 50 Hz is causing issues. A voltage transformer will not correct this issue for you as of this writing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Rigby5
Rigby5
Explorer

Posted: ‎2024-01-20 06:47 PM

0 Likes
0
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-20 06:47 PM

When you say you bought a transformer, it depends on what you mean by that?   If it was not a fully wired device sold as a converter, and is just a transformer, then you could have wired it wrong, perhaps with the wrong polarity or maybe just no chassis ground?  Another possibility is that the frequency could be different.  The US is 60 cycles per second, but many places are 50 cycles per second.  Going from 60 to 50 cps requires an expensive inverter, not just a transformer.  Cheap appliances like a hair dryer do not care what the cps are.  A UPS will.

Reply

Link copied. Please paste this link to share this article on your social media post.

Rigby5
Rigby5
Explorer

Posted: ‎2024-01-20 06:55 PM

0 Likes
0
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-20 06:55 PM

The outlet standard for Azerbaijan differs from the US not only in voltage, but also in frequency.  Their 50 cycle per second power will work on simple devices like a hair dryer, but not on a 60 cycle UPS.  You need an expensie inverter that also converts frequency, not just a voltage transformer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore