UPS runs on battery mode because building wiring fault light is on?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS runs on battery mode because building wiring fault light is on?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
7
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

UPS runs on battery mode because building wiring fault light is on?

I just bought an APC XS1300 a few days ago, however, whenever I plug it to any of my wall outlet, the building wiring fault indicator is on, and when I turn on the APC, it runs on battery directly instead of running on the utility power. Is that because of the builidng wiring fault? Any solutions?

Message was edited by: ngeddie

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

Sammak,

You don't want to go into your UPS for any reason, as it'll void the warranty and it'll be dangerous if you aren't careful.

APC sells 50hz units. You would want to get the appropriate model.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

The Building Wiring Fault indicates one of three things:

Loose or Missing Ground
Overloaded Neutral
Reversed Polarity

However, the UPS should stay online even though the LED is lit.

You might want to follow the steps in the manual to manually adjust the sensitivity to Low to see if it resolves that problem.

Do you have any other APC devices in the residence? Do you have anywhere else you can plug this UPS into?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

My situation is kinda unique, my main power supply is 220V and 50hz, and I step that down to 110V using a 1000watt transformer, and my APC is plugged to the transformer, however, whenever I turn on the APC, it runs on the battery, and the LED indicator tells me that the input voltage is 109-112V and the frequency is 57hz, so the tranformer is working, but for some reasons the APC is running on battery mode. I have tried to manually adjust the sensitivity to low, but the problem still exists.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

Did you install the software and see what the transfer points are currently set to?

The UPS should have AVR Boost to suffice for the 109-112VAC range.

Message was edited by: The Notorious K.M.P.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

You should be careful while pluging anything that has surge protection buitl-in on a step down transformer. If you reverse the power transformer polarity or the wiring polarity inside the wall outlet (Phase-Neutral) does not follow the code the step-down transformer outlet would show 220V between neutral and ground. If the MOVs inside the unit is dimensioned for 110-120V, it would blow up instantly if the ground is missing. If the ground is available, the MOVs would be in conducting state for good between neutral and ground which is a code violation in many countries. Why this happen? Read about it here:

http://www.gson.org/stepdown/

I don't know if your problem could be related to this, but check with a multimeter or a voltmeter the voltages between Phase-Neutral and neutral-ground. Between neutral ground it would be ideally at 0 volt, if it is 220V, things are very wrong there.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

also, beware that the UPS will go to battery if the frequency is out of range. acceptable frequency for this particular UPS is 60 Hz +/- 3 Hz..if its hovering around 56-57 that would cause it to go to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

i have the same problem

but i checked the frequency is 50hz not 60hz

so is there any solution to fix it by changing some components in the main ups board to be able to work in 50hz

i can do it myselfy or throught your local dealer in egypt.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

0 Likes
0
3062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:29 PM . Last Modified: ‎2024-03-22 04:38 AM

Sammak,

You don't want to go into your UPS for any reason, as it'll void the warranty and it'll be dangerous if you aren't careful.

APC sells 50hz units. You would want to get the appropriate model.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore