Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS fails scheduled tests, passes initiated tests

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS fails scheduled tests, passes initiated tests
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS On-Line

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
ElectricAvenue
ElectricAvenue
Explorer

Posted: ‎2022-10-13 02:23 PM

0 Likes
1
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-13 02:23 PM

UPS fails scheduled tests, passes initiated tests

Hi, we have a Smart-UPS X 1500 with an external battery module.


 08/30/2022 01:42:35 Device UPS: Self-Test started by automatic timer.

 08/30/2022 01:42:45 Device UPS: At least one faulty battery exists.

 

And today (6 weeks later) we got the same fault.

1. Problem is, I can reproduce it. Whenever I initiate a self-test, it passes. I tried 4 times already.

 

2. "At least one faulty battery exists." Okay, great. Which one? Do I really have to disconnect the external battery just to test? And of course I can't, because the test passes…

 

3. We also saw self-test event "started by front panel". Except that the room is locked, and no one touched the UPS. (After inquiring with staff and surveying the room, I have no reason to believe anybody was near the UPS.)

 

This unit runs our core switch, internet, firewall etc. So I hope there are some ways to take care of this instead of scheduling a major maintenance window to take the unit down.

 

Thanks

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JonPro
JonPro Troubleshooter
Troubleshooter

Posted: ‎2022-10-13 06:50 PM

0 Likes
0
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-13 06:50 PM

Hi @ElectricAvenue 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience this has caused.

 

Aside from doing a self-test while the external battery pack is disconnected, my other recommendations are as follows:

  • Reseat the connector of the external battery pack.
  • Reseat the internal batteries of both the UPS and external battery packs.

 

Those are the procedures that can be done without disrupting the operations.  The recommendations below would require you to schedule downtime.

  • Brain dead the UPS.
  • Upgrade the UPS to the latest firmware

 

I have provided the FAQ articles below for you to review.

  • Video: How to perform a cold start and brain dead on Smart-UPS 
  • How do I update the firmware of my CSH, SCL, SMC, SMT, SMTL, SMX, SRT, SRTL, XP, and XU series Smart... 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore