Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84584members
353853posts

UPS does not recognize AC power is back on after interruption

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
Macrel_apc
Crewman
Crewman
0 Likes
2
124

UPS does not recognize AC power is back on after interruption

This was originally posted on APC forums on 5/3/2008


I just replaced my battery in my UPS Backup XS 1000.

Everything appeared to be working, but when I perform a self test or if I simply unplug the UPS from the AC power and plug it back in again, the UPS does not recognize that AC power has returned,_ and continues on the battery. It then hybernates my PC and stays on battery power.

Powering the UPS off and on again results in the orange battery light being ON and the green AC power flashes a few times and then turns off.

Only after unplugging the computer and monitor and plugging them in somewhere else and turning the UPS off and on again, does the green AC LED stay on. The battery indicated 100% charge initially, this dropped to about 40% while on battery power and now the battery is charging ... it is now at 60%, showing 9 minutes of battery power available.

Whay does the UPS not recogzie when AC power is restored? It used to work before battery replacement. I also incidentally upgraded the software from 1.5 to 2.0 after replacing the batteries.

Tags (3)

Accepted Solutions
Macrel_apc
Crewman
Crewman
0 Likes
0
124

Re: UPS does not recognize AC power is back on after interruption

This was originally posted on APC forums on 5/9/2008


Hi EZ Button. Thanks for your response.

1) I charged the battery for 24 hours and retried the self test and it worked.

2) I tried the unplug test with the cable disconnected. After reconnecting the power, the battery stayed on (orange light) and the computer went into hybernation. Once the computer was off, the UPS eventually returned to AC power (green light came on).

3) I tried the self test again. It worked, but it took a long time (about 30 seconds after the self test had completed) for the UPS to realize that it had AC power again.

4) AC power is aaat 120V pretty consistently.

5) Will try remaining suggestions.

Thx

M

Message was edited by: Macrel

See Answer In Context

2 Replies 2
EZ_Button_apc
Commander
Commander
0 Likes
0
124

Re: UPS does not recognize AC power is back on after interruption

This was originally posted on APC forums on 5/5/2008


Try doing a pull plug test without the USB communication cable attached. Does it still stay on battery when you plug it back in?

Also, what does the software list as your input voltage. You may want to try raising and lowering your transfer points to on battery through the software to the max values. Also adjust your sensitivity to low for your testing.

Macrel_apc
Crewman
Crewman
0 Likes
0
125

Re: UPS does not recognize AC power is back on after interruption

This was originally posted on APC forums on 5/9/2008


Hi EZ Button. Thanks for your response.

1) I charged the battery for 24 hours and retried the self test and it worked.

2) I tried the unplug test with the cable disconnected. After reconnecting the power, the battery stayed on (orange light) and the computer went into hybernation. Once the computer was off, the UPS eventually returned to AC power (green light came on).

3) I tried the self test again. It worked, but it took a long time (about 30 seconds after the self test had completed) for the UPS to realize that it had AC power again.

4) AC power is aaat 120V pretty consistently.

5) Will try remaining suggestions.

Thx

M

Message was edited by: Macrel