Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS does not auto shutdown PC.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS does not auto shutdown PC.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
9
2963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

UPS does not auto shutdown PC.

Hello ppl. I recently purchased an APC BE650Y UPS. Plugged in the cables, the USB, installed the PowerChute software for windows XP. The software recognizes the UPS, did a dry run with a power cut and the UPS displays whether the PC is on Power or Battery.
Now I edited the auto shutdown part to "Shutdown my PC when it has been on battery backup power for 5 mins". Did a dry run but the UPS did not shutdown the PC even after it was on for about 7 mins. The box where it says 'Estimated time before shutdown' mentioned the time as -- mins. My question is why did the UPS not auto shutdown the PC automatically?

Thanks in advance for answering 🙂

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

You should be able to go into your Local Policy settings via Administrator Tools in your control panel and turn on all System Event auditing, etc. If Windows is given a shutdown command it should show up in Windows specific logs or System logs, viewable through the Event Viewer in the Control Panel -> Admin Tools.

Yes, Anti-Virus tools can cause issues with our software, so please disable them for testing. They can control what services have what control over the system in many cases.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

What operating system are you running, and what version of PCPE is currently in use? Are you using the USB cable that came with the UPS or your own? Also, have you ever experienced any "lost communication" messages from the software? Many of our software offerings have built in delays to prevent a premature shutdown from causing issues with the OS...did you plug the UPS back in right at the 7 minute mark?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

OS - Windows XP, Version being used is 2.0, this is the one which came in the cd along with the UPS. I'm using the USB cable that came with the UPS. Haven't experienced any lost communication messages from the software. I ran the UPS for more than the scheduled time set in PowerChute Software but it didn't shut down the PC.
Thanks for replying.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

Are there any events shown in the Windows event log that relate to the OS shutting down or even any programs closing? You said that the UPS said it was on battery but did PowerChute recognize the power event in its own "events" display (should say "Blackouts = 1" basically)? Also, when looking at your taskbar do you have a different battery icon as if Windows itself thinks the PC is laptop or has a battery? If you go to "Power Options" in your Control Panel do you have a Power Meter tab that shows a battery charge level or the ability to set any on battery alarms?

Please paste a screenshot of the "Technical Details/Data" and "About" screens within PowerChute, and also a screenshot of your Device Manager in Windows showing the extended/expanded information for "Batteries" and "HID Devices".

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

Yes PowerChute did recognize the blackout. When I put back the power on, a notification came that the UPS is running on AC Power. Evident from the SS




Technical Details:

Power Options:

About:

Device Manager:

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

Does your Computer hibernate properly when you do it manually? Is the Hibernation enabled in Power Options?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:37 AM . Last Modified: ‎2024-03-22 02:24 AM

Yes Hibernation is enabled in Power Options. Any other ideas?
Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

Did you install PCPE as the local system Administrator? Also, can you do another test after making sure Windows is logging System Events? There should be some record of the software interacting with the operating system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

Yup, I'm the only user/Admin. See this SS.. it shows its running on battery with shutdown time as zero but the system continues to work as i type this.

And how do I make sure that Windows is logging System Events? Is there a chance that my Firewall (Zone Alarm) or Antivirus (Nod32) are interfering the PowerChute software? I don't get any notification in zonealarm asking for access, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Erasmus_apc
Contributor

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

0 Likes
0
2963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:38 AM . Last Modified: ‎2024-03-22 02:24 AM

You should be able to go into your Local Policy settings via Administrator Tools in your control panel and turn on all System Event auditing, etc. If Windows is given a shutdown command it should show up in Windows specific logs or System logs, viewable through the Event Viewer in the Control Panel -> Admin Tools.

Yes, Anti-Virus tools can cause issues with our software, so please disable them for testing. They can control what services have what control over the system in many cases.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore