UPS Smoking, Leaking, Emitting Popcorn-like Sound -- Possible Source?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS Smoking, Leaking, Emitting Popcorn-like Sound -- Possible Source?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
4
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

UPS Smoking, Leaking, Emitting Popcorn-like Sound -- Possible Source?

Hi folks,

I have a BE650R that has served me well for a while (it's still under warranty) and just gave its first -- and evidently last -- sign of trouble this morning.

I had turned off, unplugged, and moved the unit a few days ago in order to throughly clean the area around my desk. The unit had been moved to the linoleum floor near the entrance to my apartment. There were no loads connected at all to it.

This morning, I awoke to the sound of an intermittent, weak-sounding beeping coming from the UPS. It beeped once every minute or two (unfortunately, I was a bit disoriented due to it being rather early in the morning and didn't have the presence of mind to time the intervals between the beeps). I thought that the battery had discharged over the last several days and the unit was signalling a low-battery condition and so I plugged it into the wall outlet and got back into bed. I did not push the power button -- it remained powered off but charging.

Several minutes later I awoke again, this time to a sound not unlike that of popcorn being popped. I immediately went to the UPS and noticed it sitting in a puddle of a thick, clear liquid and emitting smoke from its outlets. I immediately tripped the circuit breaker for that outlet, donned rubber gloves, and unplugged the UPS from the wall outlet. Upon opening the battery compartment, I was presented with more clear, thick liquid. I disconnected the battery, separated it from the UPS and, using paper towels, spent the next hour or so cleaning up the liquid.

Upon closer examination, there is a small hole in the plastic body of the unit on the "surge protection only" side (see picture). It appears as though the plastic body had melted. Due to the haste in which I reacted, I did not notice if the hole was the source of the liquid or if the liquid was emitted from the vents on the body.

As an experiment, I placed a small amount of baking soda in a sample of the liquid. It dissolved, but did not react in any other way. If the liquid were an acid, I assume that there would be some sort of reaction (e.g. bubbling). The battery does not appear to be bulged or otherwise damaged. Holding the battery at various angles and positions does not result in any liquids spilling from it. My multimeter reads the open-circuit voltage of the post-incident battery to be 12.98 volts, so the battery clearly has some electrolyte.

Any thoughts as to what could have caused this dramatic event? Any ideas of the source of the liquid, any special disposal considerations, and any thoughts on how harmful it may be? While I did wear gloves, I have no respiratory protection other than an open window and a fan.

I've contacted APC and they've agreed to replace the unit under warranty, but I'm curious as to the source of the problem.

I can provide additional photographs if requested.

Cheers!
-Pete

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • battery
  • beeping
  • leaking
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Nevermind, I guess you answered the question! I can delete the topic if you really wish to, but it's not necessary and we can just close it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Followup: The liquid does not appear to have originated in the UPS itself. As I've been moving many things around my desk recently, it's possible that I may have spilled something on or otherwise exposed the UPS to a liquid, though I have no recollection of any spill. Very strange.

Either way, many thanks to APC for their prompt handling of my phone call this morning.

If an administrator happens to read this thread, I'd appreciate it if they'd delete it. The option to delete a thread does not appear to be available to users.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

It looks like the battery may have "vented" or "gassed" and electrolytic fluid spilled out. This can happen when older/weaker batteries continue to be charged or if it gets hot, or if dirt or debris settle in around the battery. This liquid wouldn't necessarily have a high content ratio of acid (electrolytic fluid is typically a combination of hydrogen and oxygen, i.e. water) and therefore any baking soda reaction may be hardly noticeable. If the liquid got into the UPS' internal circuitry due to pressure build up, etc., who knows what could happen. The popping could have been a short caused by the liquid in the frame, or the popping could have been a fault that caused the buildup. It's hard to say, since this is a very rare occurrence and usually needs to be looked at in a test environment before deciding. The melting of the side of the UPS could have been caused by a part falling off the battery (I can't tell from the pictures) like a connector terminal, or just lots of heat during the battery venting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Nevermind, I guess you answered the question! I can delete the topic if you really wish to, but it's not necessary and we can just close it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Erasmus,

Closing it would be ideal. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of