Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ES750 - why can't the master controlled outlets also be on backup power?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES750 - why can't the master controlled outlets also be on backup power?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
4
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

ES750 - why can't the master controlled outlets also be on backup power?

I like the master control feature on the ES750--if i plug in my monitor and speakers to those outlets, they shut down when the PC shuts down. But then, when the UPS goes over to battery power, I don't have the use of those devices (especially the monitor). Is there a reason why those outlets couldn't have also been set up to go over to backup power?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • backup
  • control
  • es750
  • master
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

0 Likes
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

My thanks for the replies. However, the question I was seeking an answer for was why the UPS couldn't have been designed so that some outlets were both "master controlled" and battery backed. I'm sure that there must be a reason, so I was wondering what it was.

BJ

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Billy,

I've talked to one of the product specialist for this UPS and what they have told me is that some of future APC products will feature an additional controlled by master outlet which is battery powered. A battery back-up is designed to provide power to the most critical devices during a power outage. Any none essential devices on the battery side would consume energy which might otherwise have provided more runtine for the critical devices. This is one of the reason why the early design of controlled by master outlet is on the surge side.

For the release date of those UPS that offers controlled by master feature outlet on the battery side, I can say that it is still a work in progress and no definite release date yet.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

0 Likes
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:15 AM

Welcome to the APC Forum Billy.

Thanks for your feedback. I found this document on the APC web, hope you could find some helpful information [http://www.apcmedia.com/salestools/JLAE-7DZLB3_R0_EN.pdf]. I would tell the customer that those equipment that they want to be in sync with the UPS state but does not require to remain ON during a power problem can be connected on the Controlled Outlets. I would try to solicit for other opinion regarding the controlled by outlets feature.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

0 Likes
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

Billy,

The Master Control technology is used to conserve energy when the Computer is not in use. Most of the Monitors in the Industry will enter into Power Saving mode automatically if it does not receive signal from the CPU. Therefore, I would not plug the Monitor into the Master Controlled outlet as it goes to Power Saving automatically whenever the CPU does not send the signal to it.

Devices like Printer consume power from the Power Source even when the Computer is not in use. So these type of equipment need to be plugged into the Master Controlled outlets in order to save the energy when the Computer is not in use. Please view the UPS user manual for more information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

0 Likes
0
3858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:33 AM . Last Modified: ‎2024-03-22 03:14 AM

My thanks for the replies. However, the question I was seeking an answer for was why the UPS couldn't have been designed so that some outlets were both "master controlled" and battery backed. I'm sure that there must be a reason, so I was wondering what it was.

BJ

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore