Hello,
I have a UPS that displays error code P.16. I tried to find information about this error, but I didn't. Before calling support I wanted to try to resolve if possible.
Does anyone know this error code and the solution?
Regards,
Fernando Moreira
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-15 04:12 AM
Hi @Anonymous user
Let me apologize first for the inconvenience this has caused. The P.16 error also refers to Power Sys Error and is related to either a + or - DC Bus Soft Start. The UPS has detected an error upon start up from online or on battery and the UPS is not able to pre-charge the DC bus.
There are multiple reasons for this alarm, we would have to know what was the condition of the UPS when this alarm was reported for example, upon power up, when the UPS is plugged into an outlet, etc.
For troubleshooting, you can clear the alarm via the display and turn the output On again. If the issue would persist, we then recommend doing a brain-dead on the UPS. If the UPS wouldn't recover from the fault, replacing the UPS would be the recommended action.
I have provided the FAQ article below that explains how to perform the brain-dead.
Video: How to perform a cold start and brain dead on Smart-UPS (FA156611)