UPS AC output problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS AC output problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

0 Likes
6
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

UPS AC output problem

Hello,

i have the ups model APC BK650MI and i have the following problem,
when the Ups is on AC power the output is 220 Volts (Thats ok) but
when i disconnect AC power output drops toy 170 Volts.
The battery of the ups is new and checked.
Does this problem means that i have electronic problem ?

Please help ...

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

Yes this unit dropping load when battery power. What should I do now?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

0 Likes
0
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

Hi
Can I talk You directly?
shindvs@gmail.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

0 Likes
0
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:11 AM

infrared wrote:
I measure the voltage with a voltmeter (NOT true RMS). When the Ups is on the ac voltmeter says 226 volts witch is OK but when i plug of the AC (ups is on battery ) then
volts are dropped to 170 volts (having or not load on the ups). If i have load then the connected device (a simple PC for example) turns of immediately when AC power disconnects
I open UPS and i measure the battery and its says 13.7 volts and i think is OK besides the battery is 2 days old.
Is this normal ?
Yes, the voltage reading is normal. You're reading 226v on AC power, because it's sinusoidal. You're reading 170v on meter, because the meter can't properly read the modified squarewave.

It's not normal that your PC shuts off when you disconnect the AC to UPS. Does the UPS shut off as well?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:33 PM . Last Modified: ‎2024-03-26 01:10 AM

I measure the voltage with a voltmeter (NOT true RMS). When the Ups is on the ac voltmeter says 226 volts witch is OK but when i plug of the AC (ups is on battery ) then
volts are dropped to 170 volts (having or not load on the ups). If i have load then the connected device (a simple PC for example) turns of immediately when AC power disconnects
I open UPS and i measure the battery and its says 13.7 volts and i think is OK besides the battery is 2 days old.
Is this normal ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
2475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

Infrared,

How are you measuring the output? This unit will output a stepped approximated sine wave when on battery power. You will need a true RMS voltmeter to get an accurate reading of the voltage here.

Does the unit drop the load when on battery power?

You definitely want to read into kbase 1493:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1493&p_created=1010390400&p...

null

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

The power quality from that and many other consumer UPSs isn't anywhere near as good as the main line. The output on UPSs are almost always modified square wave unless otherwise stated.

To measure the voltage on a modified squarewave inverters and UPSs, you'll need a True RMS meter. Not advocating for one brand, but an example is the Fluke 87 series. Multimeters are almost always "typical responding" or not true RMS. True RMS is a feature most meter manufacture would make sure to get printed on the front cover.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
2476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-26 01:10 AM

Yes this unit dropping load when battery power. What should I do now?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore