Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Transfer switch info requested

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Transfer switch info requested
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
5
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

Transfer switch info requested

I am interested in our purchasing a transfer switch to use with 2 Honda EU 2000i and companion unit connected with parcel cables.  What is the maximum size transfer switch that I can use with these generators?  I understand that the UTS6 only has 4 120 circuits available since 2 of them are for 240 use.  If I am not correct, please let me know. I would prefer to use the 10 circuit switch, which would only give me 8 circuits???

 Thanks!

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

The UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps prepaidgiftbalance.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

Hi Allen,

Since the output of the Honda EU 2000I is 120 Volts only, the appropriate UTS model to use with a generator like this is the UTS6H which only requires 120 Volt input power from the generator. All other UTS models require 120/240 Volt generator connections to operate. The UTS6 has 6 120 Volt outputs, while the UTS6BI and UTS10BI allocate 2 of their outputs to provide 1 240 Volt output.

There are two issues to consider-- 1) the UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps, and 2) unfortunately, it appears APC has discontinued production of the UTS6H, however there may still be ways for you to buy one, maybe from a retailer with existing stock or a used unit from EBay or Craig's List.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

It looks like the UTS 6H may be a good option;however, this unit is being discontinued, which is concerning.  Apparently, the UTS 6, which is only 20 amps is the replacement.  Additionally, I can not get a clear answer if this transfer switch can be used with GFCI outlets?  

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

Hi Allen,

I'm not sure why Amazon has this unit listed as Discontinued, as I am unaware of APCs plan to do so. The UTS6 requires a 240vac input even though it only outputs 120vac circuits, so this panel would not be suitable for your configuration. The only solution for a 120vac Generator would be the UTS6H. Additionally, the UTS can be used with GFCI outlets, but can not be used with GFCI/AFCI circuit breakers.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

Amazon (and other) seller misinformation aside, the APC website no longer provides any information on the UTS6H, strongly *suggesting* this particular model is no longer manufactured. I think the whole UTS product line would benefit from better documentation of features and operation, not only in third party marketing, but even by APC on their website and in the user manuals.

Just my 2 cents worth!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

The UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps prepaidgiftbalance.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of