Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Transfer switch info requested

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Transfer switch info requested
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
aah924_apc
aah924_apc
Cadet

Posted: ‎2021-06-29 06:06 PM

0 Likes
5
301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

Transfer switch info requested

This was originally posted on APC forums on 6/19/2017


I am interested in our purchasing a transfer switch to use with 2 Honda EU 2000i and companion unit connected with parcel cables.  What is the maximum size transfer switch that I can use with these generators?  I understand that the UTS6 only has 4 120 circuits available since 2 of them are for 240 use.  If I am not correct, please let me know. I would prefer to use the 10 circuit switch, which would only give me 8 circuits???

 Thanks!

Labels
  • Labels:
  • Universal Transfer Switch
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This reply was originally posted by Taylor on APC forums on 1/30/2021


The UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps prepaidgiftbalance.com

See Answer In Context

Reply
Share
Replies 5
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This was originally posted on APC forums on 6/20/2017


Hi Allen,

Since the output of the Honda EU 2000I is 120 Volts only, the appropriate UTS model to use with a generator like this is the UTS6H which only requires 120 Volt input power from the generator. All other UTS models require 120/240 Volt generator connections to operate. The UTS6 has 6 120 Volt outputs, while the UTS6BI and UTS10BI allocate 2 of their outputs to provide 1 240 Volt output.

There are two issues to consider-- 1) the UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps, and 2) unfortunately, it appears APC has discontinued production of the UTS6H, however there may still be ways for you to buy one, maybe from a retailer with existing stock or a used unit from EBay or Craig's List.

Reply
Share
aah924_apc
aah924_apc
Cadet

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This was originally posted on APC forums on 6/21/2017


It looks like the UTS 6H may be a good option;however, this unit is being discontinued, which is concerning.  Apparently, the UTS 6, which is only 20 amps is the replacement.  Additionally, I can not get a clear answer if this transfer switch can be used with GFCI outlets?  

 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This reply was originally posted by Secret on APC forums on 6/28/2017


Hi Allen,

I'm not sure why Amazon has this unit listed as Discontinued, as I am unaware of APCs plan to do so. The UTS6 requires a 240vac input even though it only outputs 120vac circuits, so this panel would not be suitable for your configuration. The only solution for a 120vac Generator would be the UTS6H. Additionally, the UTS can be used with GFCI outlets, but can not be used with GFCI/AFCI circuit breakers.

Secret Squirrel

Reply
Share
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This was originally posted on APC forums on 6/28/2017


Amazon (and other) seller misinformation aside, the APC website no longer provides any information on the UTS6H, strongly *suggesting* this particular model is no longer manufactured. I think the whole UTS product line would benefit from better documentation of features and operation, not only in third party marketing, but even by APC on their website and in the user manuals.

Just my 2 cents worth!

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:06 PM

0 Likes
0
303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:06 PM

This reply was originally posted by Taylor on APC forums on 1/30/2021


The UTS6H is rated at 30 Amps while your configuration of 2 paralleled EU2000I generators can deliver about 33 Amps prepaidgiftbalance.com

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc