Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Surge protectors

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Surge protectors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Ruger62
Ruger62
Explorer

Posted: ‎2024-09-19 06:07 AM

0 Likes
1
1079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-19 06:07 AM

Surge protectors

Hello, How much the 30 foot rule should I pay attention to regarding the distance from the outlet of the bar to the electrical panel? I have small house and the electrical outlets in our den is just on the othere sided of the wall from the panel location in the back porch. Old house (1958 ) with few  outlets in strange places on none at all. I have no choice for this location. Is the 30 foot rule there for the "protection" of cheaply made surge bars?

 Do I add in a very long extension cord to add in the 30 feet?

Thank you for your time,

Regards,

Rick

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Teken
Champion

Posted: ‎2024-09-27 09:36 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-27 09:36 AM

I’m not familiar with this so called 30 foot rule you speak of - Link?!?

 

I am also not clear what you’re asking about vs what you’re trying to do.

 

Regardless, I’m going to make a few assumptions and offer you some advice and insight as it relates to any SPD.

 

Ground: Everything related to the home’s electrical system is tied (bonded) to the most important area and that is the single point low resistance Earth Ground. 

Depending upon where you live and the codes in force the ground resistance must be below <25 Ohms.

 

SPD: A surge protection device (SPD) comes in four types. They are each designed and made to offer surge / spike protection based on their final installation.

 

Type 1: These devices are installed at the service entrance (meter).

 

Type 2: These devices are installed at the service panel (breaker).

 

Type 3: These are installed at the Point of Use such as at the outlet.

 

Type 4: These are installed inline prior to a device / circuit. 

If you buy any Type 3 SPD that has a cord set. It will have a specific cord length to meet its requirements to carry the maximum load (current) with the minimum loss of voltage to meet its power handling.

 

Meaning they are NOT intended to be extended with an extension cord! ☝️ If you do use an extension cord that cord set must be the correct (AWG) gauge to meet the same ampacity, voltage drop, power handling for the given distance.

 

Meaning if the SPD has a 12-3 cable you should not use a 14-3, 16-3, 18-3 cord set! Lastly, every thing has a derating specification which calls out 80% is the maximum continuous allowed.

 

Let me know if you need more information or clarification. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore