Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

SmartUPS10000 Battery problem - Info Required

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS10000 Battery problem - Info Required
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
9
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

SmartUPS10000 Battery problem - Info Required

This was originally posted on APC forums on 7/13/2010


I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

Labels
  • Labels:
  • Universal Transfer Switch
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/13/2010


I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

See Answer In Context

Reply
Share
Replies 9
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/14/2010


What I was looking for was more technical information on the unit and that seems hard to find.
For example, does it only need two battery packs to actually function? That would only be 200VDC.
And does it use 4 packs so that it can extend it's time?

With another UPS I had previously, I had built a complete external battery setup. In that case, it was 20 marine batteries, using external intelligent charger and connected to the UPS via breaker. If I can't trust the UPS, I know I could trust my own external batteries but I've seen suggestions against using it because the unit would not be able to calibrate etc. That would not matter much to me, so long as I knew my batteries were working well, I only need a few minutes of backup power for the geny to kick in.

Mike

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/15/2010


So after a couple of days now, the voltage has gone back to 216VDC for Batteries. There is 15 minutes of run time.
If anything, I suppose I should be able to get some sort of warning that it won't be able to handle it when I shut the power off?
I need at least 30 seconds for the geny to kick in then the UPS needs to last long enough to sense power and come back off of the batteries.

Just trying to figure out how to test this without taking the load down as it's a ton of work to get everything back up.

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/15/2010


Anyone?
Also, I don't suppose there is any way of testing to see if the batteries will hold the load without actually putting the load on the batteries? I mean, there is no internal sensing that would let me know this without accidentally taking the load down if the batteries won't hold?

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/15/2010


>
Also, I don't suppose there is any way of testing to see if the batteries will hold the load without actually putting the load on the batteries? I mean, there is no internal sensing that would let me know this without accidentally taking the load down if the batteries won't hold?
>

I don't know the answer to your other questions, but yes, the only way for a SmartUPS to test the battery is to put the load on them. Batteries can appear normal until you try drawing significant current out of them.

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/15/2010


Ok, just wanted to confirm. Guess we'll give it a shot tonight.

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/15/2010


I did it from remote, I read that doing a calibration didn't put the unit on batteries. You mean it did? If that's the case, nothing went down.

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/16/2010


Didn't last very long on the batteries so guess I need new ones, again.
Worse is that while the batteries discharged very quickly, it did last long enough for the geny to kick in.
Also, when I turned the utility back on and it switched back to utility, it dropped part of the load, but not all of it.

I then switched out two of the packs which aren't known to be brand new batteries such as the gruber and like the other test, was able to pass a recalibration test but am not sure if it'll pass a load test. Guess there's only one way to find out again.

I really wish I could simply use externals, these little batteries are ridiculous.

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/16/2010


I see in an above post you ran a calibration - how long did it stay on battery?
That should be the amount of run time you can expect if an outage occurs.
I didn't know that a calibration meant that the UPS tests how long it can stay on it's batteries. It was maybe two minutes at most.
How long have these batteries been in use? Months? Years?
At this point, I've mixed them up so am not sure. I did a load test on every battery in two packs this morning and all of them were in the 'Weak' state. The two packs which are not the new Gruber batteries were supposed to be new but I suspect they are not at this point. Looks like I should get 16 new batteries.

Mike

Reply
Share
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 09:10 PM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 09:10 PM

This was originally posted on APC forums on 7/13/2010


I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc