Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SmartUPS10000 Battery problem - Info Required

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS10000 Battery problem - Info Required
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
9
3529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

SmartUPS10000 Battery problem - Info Required

I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

What I was looking for was more technical information on the unit and that seems hard to find.
For example, does it only need two battery packs to actually function? That would only be 200VDC.
And does it use 4 packs so that it can extend it's time?

With another UPS I had previously, I had built a complete external battery setup. In that case, it was 20 marine batteries, using external intelligent charger and connected to the UPS via breaker. If I can't trust the UPS, I know I could trust my own external batteries but I've seen suggestions against using it because the unit would not be able to calibrate etc. That would not matter much to me, so long as I knew my batteries were working well, I only need a few minutes of backup power for the geny to kick in.

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

So after a couple of days now, the voltage has gone back to 216VDC for Batteries. There is 15 minutes of run time.
If anything, I suppose I should be able to get some sort of warning that it won't be able to handle it when I shut the power off?
I need at least 30 seconds for the geny to kick in then the UPS needs to last long enough to sense power and come back off of the batteries.

Just trying to figure out how to test this without taking the load down as it's a ton of work to get everything back up.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

Anyone?
Also, I don't suppose there is any way of testing to see if the batteries will hold the load without actually putting the load on the batteries? I mean, there is no internal sensing that would let me know this without accidentally taking the load down if the batteries won't hold?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

>
Also, I don't suppose there is any way of testing to see if the batteries will hold the load without actually putting the load on the batteries? I mean, there is no internal sensing that would let me know this without accidentally taking the load down if the batteries won't hold?
>

I don't know the answer to your other questions, but yes, the only way for a SmartUPS to test the battery is to put the load on them. Batteries can appear normal until you try drawing significant current out of them.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

Ok, just wanted to confirm. Guess we'll give it a shot tonight.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

I did it from remote, I read that doing a calibration didn't put the unit on batteries. You mean it did? If that's the case, nothing went down.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

Didn't last very long on the batteries so guess I need new ones, again.
Worse is that while the batteries discharged very quickly, it did last long enough for the geny to kick in.
Also, when I turned the utility back on and it switched back to utility, it dropped part of the load, but not all of it.

I then switched out two of the packs which aren't known to be brand new batteries such as the gruber and like the other test, was able to pass a recalibration test but am not sure if it'll pass a load test. Guess there's only one way to find out again.

I really wish I could simply use externals, these little batteries are ridiculous.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

I see in an above post you ran a calibration - how long did it stay on battery?
That should be the amount of run time you can expect if an outage occurs.
I didn't know that a calibration meant that the UPS tests how long it can stay on it's batteries. It was maybe two minutes at most.
How long have these batteries been in use? Months? Years?
At this point, I've mixed them up so am not sure. I did a load test on every battery in two packs this morning and all of them were in the 'Weak' state. The two packs which are not the new Gruber batteries were supposed to be new but I suspect they are not at this point. Looks like I should get 16 new batteries.

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
mlewis_apc
Contributor

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

0 Likes
0
3529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:44 AM

I am trying to find information on what the technical data should be on batteries for the above unit.
I replaced all of the batteries but the red LED remains on. I also notice that the Battery voltage has not changed and am trying to find out what it should be.

Last Battery Transfer: Unacceptable utility voltage rate of change
Internal Temperature: 90.3°F
Runtime Remaining: 15 minutes

Power
Input Voltage: 236.1 VAC

Bypass Input Voltage:
Output Voltage: 207.0 VAC
Current:
Input Frequency: 60.01 Hz

Load
Load Power: 52.0 %Watts
Apparent Load Power: 43.0 %VA
Load Current: 20.79 Amps

Battery
Capacity: 100.0 %
Battery Voltage: 216.0 VDC
External Batteries: 1

There are 4 battery packs in the unit. What voltage should I be seeing? It was around the same before I replaced the batteries.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore