The on-battery LED is flashing on my SmartUPS 700 but the manual does not mention this option.
Mains voltage is going to the unit and is normal according to the LED bar graph.
There is no beeping from the uunit.
What is the problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
If the model number on the back of the unit only says "SU700" then it is a domestic U.S. model. If it says "SU700I" on the back then the 247.x voltage is perfectly fine. Since this sounds like it's been working for you in the past I doubt it is just a "SU700", but please check.
Assuming this is an SU700I, at this point I would recommend keeping the serial communication cable unplugged from the UPS and monitor the UPS' behavior. If this seems to truly prevent that LED from blinking I would consider purchasing another serial communication cable (part# is 940-0024). You could also try swapping the serial connection to another computer (or serial port) just to make sure there is no issue with the physical connection on the computer/server side. Long story short, barring any unexpected info this seems to be a serial/communication bus issue.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:01 PM . Last Modified: 2024-03-22 04:28 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:01 PM . Last Modified: 2024-03-22 04:28 AM
Well the reset worked, so I plugged it all in and all was fine for a while until the LED started flashing again.
I've disconnected the serial lead and that has stopped the LED flashing but now of course I cannot get my server to close down in the event of a power cut!
Any ideas?
Voltage in is 247.9 v which is spot on for the UK.
Message was edited by: spile
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:01 PM . Last Modified: 2024-03-22 04:27 AM
How long has the on-battery LED been flashing? The UPS will periodically run a self test and this will cause the on-battery LED to blink for a short period of time (around 8-15 seconds).
When you hold down the test button to get the voltage, what exactly is indicated?
What is the serial # on this unit and when was the battery last replaced?
Are you running any of our PowerChute software by any chance?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:01 PM . Last Modified: 2024-03-22 04:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:01 PM . Last Modified: 2024-03-22 04:27 AM
How long has the on-battery LED been flashing? The UPS will periodically run a self test and this will cause the on-battery LED to blink for a short period of time (around 8-15 seconds).
Since I got home about 2 hours
When you hold down the test button to get the voltage, what exactly is indicated?
Holding down the Tes button doesn't do anything - The voltage LEDs are already lit and show normal voltage 240v
What is the serial # on this unit and when was the battery last replaced?
NS9903086109 March 2008
Are you running any of our PowerChute software by any chance?
No but it is connected to a Windows Home Server by a serial lead.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
just wondering also - its definitely the "on battery" and not the "replace battery" LED, correct?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Model = SU700
Using the Windows Home Server (Windows 2003) native UPS facility.
The LED that is flashing is the middle LED of the second row ie the one with the sinewave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
If the model number on the back of the unit only says "SU700" then it is a domestic U.S. model. If it says "SU700I" on the back then the 247.x voltage is perfectly fine. Since this sounds like it's been working for you in the past I doubt it is just a "SU700", but please check.
Assuming this is an SU700I, at this point I would recommend keeping the serial communication cable unplugged from the UPS and monitor the UPS' behavior. If this seems to truly prevent that LED from blinking I would consider purchasing another serial communication cable (part# is 940-0024). You could also try swapping the serial connection to another computer (or serial port) just to make sure there is no issue with the physical connection on the computer/server side. Long story short, barring any unexpected info this seems to be a serial/communication bus issue.
Link copied. Please paste this link to share this article on your social media post.