Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

SmartUPS 700 on-battery LED flashing

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS 700 on-battery LED flashing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2129
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
spile_apc
Crewman spile_apc
Crewman

Posted: ‎2021-06-28 11:01 PM

0 Likes
8
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:01 PM

SmartUPS 700 on-battery LED flashing

This was originally posted on APC forums on 12/1/2008


The on-battery LED is flashing on my SmartUPS 700 but the manual does not mention this option.
Mains voltage is going to the unit and is normal according to the LED bar graph.
There is no beeping from the uunit.

What is the problem?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This was originally posted on APC forums on 12/2/2008


If the model number on the back of the unit only says "SU700" then it is a domestic U.S. model. If it says "SU700I" on the back then the 247.x voltage is perfectly fine. Since this sounds like it's been working for you in the past I doubt it is just a "SU700", but please check.

Assuming this is an SU700I, at this point I would recommend keeping the serial communication cable unplugged from the UPS and monitor the UPS' behavior. If this seems to truly prevent that LED from blinking I would consider purchasing another serial communication cable (part# is 940-0024). You could also try swapping the serial connection to another computer (or serial port) just to make sure there is no issue with the physical connection on the computer/server side. Long story short, barring any unexpected info this seems to be a serial/communication bus issue.

See Answer In Context

Reply
Share
Replies 8
spile_apc
Crewman spile_apc
Crewman

Posted: ‎2021-06-28 11:01 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:01 PM

This was originally posted on APC forums on 12/2/2008


Well the reset worked, so I plugged it all in and all was fine for a while until the LED started flashing again.
I've disconnected the serial lead and that has stopped the LED flashing but now of course I cannot get my server to close down in the event of a power cut!
Any ideas?
Voltage in is 247.9 v which is spot on for the UK.

Message was edited by: spile

Reply
Share
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:01 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:01 PM

This was originally posted on APC forums on 12/1/2008


How long has the on-battery LED been flashing? The UPS will periodically run a self test and this will cause the on-battery LED to blink for a short period of time (around 8-15 seconds).

When you hold down the test button to get the voltage, what exactly is indicated?

What is the serial # on this unit and when was the battery last replaced?

Are you running any of our PowerChute software by any chance?

Reply
Share
spile_apc
Crewman spile_apc
Crewman

Posted: ‎2021-06-28 11:01 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:01 PM

This was originally posted on APC forums on 12/1/2008


How long has the on-battery LED been flashing? The UPS will periodically run a self test and this will cause the on-battery LED to blink for a short period of time (around 8-15 seconds).
Since I got home about 2 hours

When you hold down the test button to get the voltage, what exactly is indicated?
Holding down the Tes button doesn't do anything - The voltage LEDs are already lit and show normal voltage 240v

What is the serial # on this unit and when was the battery last replaced?
NS9903086109 March 2008

Are you running any of our PowerChute software by any chance?
No but it is connected to a Windows Home Server by a serial lead.

Reply
Share
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This was originally posted on APC forums on 12/1/2008


spile wrote:

When you hold down the test button to get the voltage, what exactly is indicated?
Holding down the Tes button doesn't do anything - The voltage LEDs are already lit and show normal voltage 240v
What is the model number on your Smart-UPS 700? This should be on the back/bottom of the UPS near the serial number.
spile wrote:

Are you running any of our PowerChute software by any chance?
No but it is connected to a Windows Home Server by a serial lead.
Are you using native UPS monitoring/shutdown with this serial connection? Long story short: is it necessary for this to be connected?

I'm thinking this could be a unit fault or a communication issue involving the serial port. Final question: any accessories installed in the UPS?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This reply was originally posted by Angela on APC forums on 12/1/2008


just wondering also - its definitely the "on battery" and not the "replace battery" LED, correct?

Reply
Share
spile_apc
Crewman spile_apc
Crewman

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This was originally posted on APC forums on 12/1/2008


Model = SU700
Using the Windows Home Server (Windows 2003) native UPS facility.
The LED that is flashing is the middle LED of the second row ie the one with the sinewave

Reply
Share
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This was originally posted on APC forums on 12/1/2008


spile wrote:
Model = SU700
Using the Windows Home Server (Windows 2003) native UPS facility.
The LED that is flashing is the middle LED of the second row ie the one with the sinewave


Holding down the Test button doesn't do anything - The voltage LEDs are already lit and show normal voltage 240v
I would try the following:

a) When you get a chance, unplug the load from the UPS so there is nothing plugged into any of the output outlets on the back of the UPS.
b) Turn the UPS off entirely and unplug it from the wall.
c) Hold the OFF button on the UPS to "braindead" it. You should hear a faint click from the UPS.
d) Unplug the serial cable from back of the UPS.
e) Move the UPS to a different outlet in the house/building and try turning it back on.

If these steps do not help, we could also have you adjust the sensitivity on the UPS afterwards.

In regards to the "240v" input to the unit...this unit should have 120v coming in. Any chance of measuring what the input vac is?

Reply
Share
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:02 PM

0 Likes
0
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 11:02 PM

This was originally posted on APC forums on 12/2/2008


If the model number on the back of the unit only says "SU700" then it is a domestic U.S. model. If it says "SU700I" on the back then the 247.x voltage is perfectly fine. Since this sounds like it's been working for you in the past I doubt it is just a "SU700", but please check.

Assuming this is an SU700I, at this point I would recommend keeping the serial communication cable unplugged from the UPS and monitor the UPS' behavior. If this seems to truly prevent that LED from blinking I would consider purchasing another serial communication cable (part# is 940-0024). You could also try swapping the serial connection to another computer (or serial port) just to make sure there is no issue with the physical connection on the computer/server side. Long story short, barring any unexpected info this seems to be a serial/communication bus issue.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc