SmartUPS 700 beep for many hours

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS 700 beep for many hours
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
126
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
7
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

SmartUPS 700 beep for many hours

In my home I've an old SmartUPS 700 connected to my PC and it has worked fine for years.

One month ago I've replaced the two batteries and after that something strange happens.

I've a main 220V power switch and when I've finished my job, I switch off my PC then I power off SmartUPS and then I switch off main power switch. UPS main power is no more connected to 220V

Well, starting from this moment, SpartUPS emit a short "beep" every about 10 min. for many hours (about 4-6 hours).
It's very annoying. And during night is terrible :-((

I've tried to disconnect all power cord (220V main power and loads) but nothing change. If I disconnect ups main power, ups 'beep'

UPS is working fine: if it's powered on and I disconnect 220V, my PC still working for about 15 min. without problem.
It's working also serial connection for Linux apcd daemon.

Can I stop my ups "beep" ?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

While APCUPSD has the capability to mute some of the audible alerts, I recommend trying to find the source of the problem rather than hiding the symptoms.
In my Ubuntu 8.04 Hardy Heron I've installed the package apcupsd 3.14.2 and with the command
apctest eeprom
I done the following tasks:
- perform battery runtime calibration (it works fine)
- (in EEPROM) change the battery date to today (old date was 10/06/04 )
- (in EEPROM) set the alarm delay (BEEPSATE) to 'N'

Now the beep disappeard. Really all audible message are off .
This evening I'll enable again the BEEPSTATE to previous value ( '0' ) and I'll check if UPS will emit the beep again.
I noticed you regularly turn the UPS off. I know APC UPSes are designed to be kept on so they can keep the battery topped up.
Yes, but before the battery replacement, UPS worked fine without any beep also if I turn off the UPS

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

let us know what happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

ok, so all the LEDs are off even when the UPS is on? or do you just have the UPS turned off for now since the beeping is annoying?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

i dont suppose you noticed any strange LED combinations on the front of the Smart UPS? anything flashing, any red LEDs?

and this only happened after replacing the batteries on the UPS?

in the meantime before we figure out what the issue is, you can try muting the alarm through the software if its possible with APCUPSD. i am not sure since its third party software how to go about doing it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

No strange LED flashing.
All LEDs are off

The problem appears after replacing battery.
Before the UPS was ok.

I try mute sound with APCUPSD tomorrow.

Message was edited by: ambrosa

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

While APCUPSD has the capability to mute some of the audible alerts, I recommend trying to find the source of the problem rather than hiding the symptoms.

I noticed you regularly turn the UPS off. I know APC UPSes are designed to be kept on so they can keep the battery topped up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

ok, so all the LEDs are off even when the UPS is on? or do you just have the UPS turned off for now since the beeping is annoying?
No no.
LEDs are working fine and normally when UPS is on.
When I switch off UPS, all LEDs are off. This is correct.
And when I disconnect the UPS from 220V main power, start the beep (1 beep every about 10 minutes for 5-6 hours). When I heard the "beep" , all LEDs stay off: there are no LEDs flashing during the beep.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:00 PM . Last Modified: ‎2024-03-22 04:29 AM

While APCUPSD has the capability to mute some of the audible alerts, I recommend trying to find the source of the problem rather than hiding the symptoms.
In my Ubuntu 8.04 Hardy Heron I've installed the package apcupsd 3.14.2 and with the command
apctest eeprom
I done the following tasks:
- perform battery runtime calibration (it works fine)
- (in EEPROM) change the battery date to today (old date was 10/06/04 )
- (in EEPROM) set the alarm delay (BEEPSATE) to 'N'

Now the beep disappeard. Really all audible message are off .
This evening I'll enable again the BEEPSTATE to previous value ( '0' ) and I'll check if UPS will emit the beep again.
I noticed you regularly turn the UPS off. I know APC UPSes are designed to be kept on so they can keep the battery topped up.
Yes, but before the battery replacement, UPS worked fine without any beep also if I turn off the UPS

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore