SmartUPS 1000, Battery unable to support the load problem.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS 1000, Battery unable to support the load problem.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
7
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

SmartUPS 1000, Battery unable to support the load problem.

I currently own 2 SmartUPS 1000 models.
The first one had a battery replacement over half a year ago, the second one just recently.
With the first one all went well, but the second UPS still complains about the battery that's unable to support the load (battery leds flashing).
The load didn't change at all, It's still the same machine as it is for years.
I have to admit that the ups complained several months that it needed a new battery, but since the load wasn't that critical, I've postponed it.
Also both ups' have the AP9617 smartslot card's installed.
When I googled the warning, I came across this white-paper: http://www.buyuptime.com/commerce/storefronts/buyuptime/pdf/AskTheExperts.pdf
Suggesting me that I needed to perform a manual runtime calibration.

For this I used the following technique:

- Fully (24H) charge the batteries
- Disconnected entire UPS (even the battery connector)
- Connected a reliable steady non critical load (500W light bulb)
- Disconnected all communication with the ups (removed the smartslot card, disconnected serial / usb ports)
- Reconnected the battery
- Plugged the power cord in
- Turned on the light bulb while working on AC power
- Pulled out the power cord
- Waited until the light bulb went out (UPS switched itself off)

This gave me the following result:

- The runtime for a 500W load seems normal (+- 19 minutes)
- The ups immediately gave me the 'battery critical low' warning after unplugging the power cord
- I left the UPS charging for about 2 hrs (battery indicator telling me the battery is recharged again)
- Plugged the machine (+- 29% of total ups load) back into the ups (leaving the power cord plugged in), booted the machine, the ups immediately gave me the same warning as the one I started with (battery light flashing).
Even with the management card still not inserted. (so I'm sure the ups uses its own hardware build in system to monitor the battery).

I'm all out of ideas... any help?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:13 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:13 AM . Last Modified: ‎2024-03-22 01:37 AM

Thanks for the replies.
I was able to fix it with the APCFIX.exe utility.
Your post pointed me in the right direction.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

About how long did the 500w light bulb run on battery before the UPS turned off? Was that the 19m value you reported, or did you see that in the NMC? And how does that compare to what the NMC shows as the expected runtime after running the calibration?

You'll need to reinstall the NMC to see this (or use the PCBE software) to find this setting. Then again, you said the computer creates 29% load so maybe it's already installed... unless you just remember that from before you began this procedure.

Also, what is the low battery duration value set to? What's the complete model number for this unit (SUA1000 vs SU1000, for example)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

The 19 minutes is the time the light bulb ran on UPS power.
The 29% load is the value I remembered from a previous check-up with the management card.
The expected runtime (before manual calibration) was +- 2 minutes, the same as the low battery duration setting in the management software.

Today I'm reinstalling the management card and let you know about the rest of the values.

Greetings.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

I've reinstalled the management card, and in addition to my previous post, I've gained the following values:

Last Battery Transfer: No transfers have occurred
Internal Temperature: 29.7°C
Runtime Remaining: 7 minutes
Power
Input Voltage: 230.4 VAC
Output Voltage: 231.8 VAC
Frequency: 50.0 Hz
Load Power: 30.5 %Watts
Battery Capacity: 100.0 %
Battery Voltage: 27.54 VDC
External Batteries: 0

Model: Smart-UPS 1000
Serial Number: AS0142132617
Firmware Revision: 600.1.I
Manufacture Date: 10/19/01

Self-Test: Passed on April 02, 2010
Calibration: Passed on April 01, 2010

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

So it's almost 10yrs old... Not too surprised it's a little bit off in terms of estimated runtime. The battery constants probably need to be reset. I think I've seen some posts around here from "unofficial" sources with instructions for that, though you'd be better off calling in to tech support to make sure you don't change the wrong values.

The battery bar graph shouldn't be flashing anymore though, since it should only do that when the runtime is within 2m of the low battery duration (which you said is also 2m). So as long as your runtime > 4m, it shouldn't be flashing...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

The battery bar indeed isn't flashing anymore.
But sometimes the management card still tells me that the batteries are unable to support the load.
Probably when the cpu is dooing some calculating.
Can you point me in the right direction about the reset for battery constant?
Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:12 AM . Last Modified: ‎2024-03-22 01:37 AM

Unfortunately, not really, because it's proprietary information that APC doesn't publish. [This thread|Referenced content removed] kind of outlines the discussion. You may need to call your regional tech support to get a calibration key.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:13 AM . Last Modified: ‎2024-03-22 01:37 AM

0 Likes
0
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:13 AM . Last Modified: ‎2024-03-22 01:37 AM

Thanks for the replies.
I was able to fix it with the APCFIX.exe utility.
Your post pointed me in the right direction.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore