Smart Ups RS 1500 BR1500 Overload Fault with no Load, however....

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart Ups RS 1500 BR1500 Overload Fault with no Load, however....
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-21 10:50 PM

0 Likes
9
468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 10:50 PM

Smart Ups RS 1500 BR1500 Overload Fault with no Load, however....

When turned on, the Green On-Line flashes for about 5 seconds.

Then momentarily the Yellow On-Battery comes on

Then continuous Red Overload light and continuous buzzer.

 

There is a Building Fault on since the outlet is 2-prong w/o ground.

 

However, I'm trying to test unit and have one new battery and one that is extremely weak - no load the battery pack is >26 volts.

 

It clearly drops out of On-Battery instantly, but does not light the Replace Battery light.

 

NOTE:  This unit was removed from service when I measured 135v On-Battery but it may not have been a True RMS DMM.

 

QUESTION:  I could find another battery with some life in it - I don't want to buy a new battery for a matched set only to find the unit is malfunctioning.  SUGGESTIONS?

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Teken
Janeway Teken
Janeway

Posted: ‎2024-10-22 04:35 AM

0 Likes
8
447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 04:35 AM

A True RMS meter has absolutely nothing to do with a DC measurement. ☝️ It’s near impossible you measured 135 DC volts at the battery terminal.

 

If you did it would be pretty apparent as to the physical condition of the battery cartridge! 🤦‍♂️

 

Regardless, there’s nothing you can do with the system without two good cells in place.

 

Start there and once the new battery is connected set the meter to DC (NOT) AC. Validate the system is charging the cartridge at 27.XX volts. 

Let me know . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-23 01:41 AM

In response to Teken
0 Likes
7
428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 01:41 AM

The measurement is the AC output On-Battery being 135v when the line voltage is 124v.   Since the output is not a sine wave, having a True RMS DMM is critical for an accurate measurement.  If the meter used was not True RMS, the actual RMS voltage was greater than 135v.

The weak battery was replaced and the unit still behaved the same.  

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-10-23 05:23 AM

In response to MrCreosote
0 Likes
6
415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 05:23 AM

Connect the system to a computer running APC Power Chute Software. What does the software indicate is the active fault / error codes?!?

 

While you’re in there update the battery installation date. Manually initiate a Self Test what does the system do or show in Power Chute / LCD Display?!?

 

Brain Dead: You may try to reset the internal MCU by following this procedure:

 

https://www.apc.com/us/en/faqs/FA156611/

Reply

Link copied. Please paste this link to share this article on your social media post.

MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-23 08:20 PM

In response to Teken
0 Likes
5
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 08:20 PM

When the unit is turned on, it performs the self-test and fails as I described.

I don't have the RJ45 to USB cable to connect to PC - am trying to see if a friend has one.  (if he doesn't may order one for $4 from China - will take couple weeks to get here.)

No sure about the Brain Dead procedure - the ones described have different controls than mine.  But since the unit does the Self Test when turned on, doesn't this mean it is not Brain Dead?

 

Thanks

Tom

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-10-24 08:35 AM

In response to MrCreosote
0 Likes
4
391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 08:35 AM

Hi Tom,

 

Brain Dead: This procedure is intended to clear the MCU of random faults while resetting it to a default state. 

Remove AC Mains from the wall. Disconnect the internal battery. Press and hold the power button until you hear a click / beep.

 

You may not hear anything at all either. ☝️Do this reset at least three times following the steps up above.

 

Wait for the cable to arrive and once connected to a computer system running APC PCBE / PCSS call out what active faults / error codes are displayed.

 

Please update the battery installation date and follow up with manually initiating a Self Test.

 

If it fails proceed to manually initiate a battery calibration via Power Chute Software. There must be at least 30% attached load on the outputs. 

 

More than likely both will fail to initiate and complete. If so the unit needs to be replaced as there’s an obvious internal fault. 

Let me know what you see and observe once all cables and software is installed. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-24 10:07 AM

In response to Teken
0 Likes
3
376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 10:07 AM

Can I use the Ethernet Network connection or do I need the RJ45-USB cable?  (Is there anything special about the RJ45/USB cable?)

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-10-25 06:32 AM

In response to MrCreosote
0 Likes
2
373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 06:32 AM

The Ethernet port on the unit is for surge protection only.


You’ll need to use the OEM APC USB - RJ45 cable or one you made and validated to work.

 

You’ll need to search the net to confirm the pin out and wiring.

 

As the vast majority of the APC Serial cables are wired in a proprietary manner that doesn’t comply to industry standards. 🤦‍♂️👎

 

NOTE: As an aside you need to find an outlet that provides a Earth Ground. As the system will cry and complain there’s a building wiring fault.

 

Depending upon what firmware is installed this fault may cause the system to declare a hard fault.

 

Meaning any other problems you have won’t clear until this safety requirement is met! ☝️

Reply

Link copied. Please paste this link to share this article on your social media post.

MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-25 09:36 PM

In response to Teken
0 Likes
0
319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 09:36 PM

Proper grounded outlet doesn't make any difference:  when started On-Line flashes for about 5 seconds, then On-Battery for a split second, and then Overload flashing red.

Starting with unit unplugged, does the same except no On-Line, it starts with the split second On-Battery and ends up the same.

 

That APC proprietary RJ45 to USB - do all such APC cables have the same pin-outs?  or are there different APC RJ to USB types?

Reply

Link copied. Please paste this link to share this article on your social media post.

MrCreosote
Crewman MrCreosote
Crewman

Posted: ‎2024-10-27 07:25 PM

In response to Teken
0 Likes
0
319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-27 07:25 PM

I may invest in a data cable or two.  I have a bunch of ES 725's that also have that port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of