Smart-UPS or Back-UPS for Proliant ML370

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS or Back-UPS for Proliant ML370
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
3
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:10 AM

Smart-UPS or Back-UPS for Proliant ML370

I am relative newbie in IT.
In my current job we have a number of servers running off of APC SmartUPSs. However these UPS's from what i'm aware of are not currently being monitored. I do not have any exp with monitoring server loads etc. But I would like to improve my understanding of it esp the Smart-UPS line.

so here's what i have done and why i need some direction. I was able to secure 2 really old Compaq ML370 server running Windows 2000. they both have 2 P3 CPUs, 5 scsi3 hdd with raid 5, and a cdrom drive with 512 mb ram. I'm thinking of purchasing the Back-ups 1300 XS, then connecting the servers to it and practice using the Powerchute software to perform diagnostic/monitoring etct.

I'm hoping that the skills i'll acquire from using Powerchute on the desktop XS model is transferable to the Server Smart-UPs line.

-q: therefore, based on what i have read online so far, do i really have to go with a Smart UPS versus a BACK-UPS if I want to monitor a Compaq ML370?
-q:what will happen if i connect the ML370 servers to a Desktop UPS(BACK-UP XS 1300)?,
-q:will i take a performance hit, or lose some monitoring functionality or will the server just not power on ?

fyi: I do realize that I can accomplish the same thing by using my PC's instead of the servers. But I'm just curious.

thx

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • management
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

Your next step would be to determine the amount of runtime that you're going to want when the UPS goes to battery for an abnormal power event. The closer you are to full capcity, the less runtime you'll receive. Right now, I'm leaning towards an SUA1500 which is I think off the top of my head, an 865 or 925W UPS. That will cover the initial inrush of the PSU's, then give you a decent amount of runtime while on battery once the PSU's go back down to a normal operating Wattage.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:10 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:10 AM

Hello,

I will answer your questions in the order in which they were asked.


-q: therefore, based on what i have read online so far, do i really have to go with a Smart UPS versus a BACK-UPS if I want to monitor a Compaq ML370?
A: If you're starting to get into the business of potentially monitoring other servers using APC Products and Software, you may want to use a Smart-UPS since you cannot use PowerChute Personal Edition with any Smart-UPS, and vice versa, cannot use PowerChute Business Edition with any new Back-UPS. Business Edition is smart-signaling with direct connections to Smart-UPS and allow for more detailed information such as data and event logging, which PowerChute Personal Edition does not.

-q:what will happen if i connect the ML370 servers to a Desktop UPS(BACK-UP XS 1300)?,
A: It would depend on how sensitive your PSU on the server is to a step-approximated sine wave. It may reboot, it may operate online with some humming from the PSU. Again, it's dependant upon the PSU's requirements.

-q:will i take a performance hit, or lose some monitoring functionality or will the server just not power on ?
A: The server will power on, but as stated before, with the Back-UPS if the PSU cooperates, you're going to have VERY limited information and diagnostics you can run on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

so what you're saying is ..the Powerchute PE is for Back-ups & PowerChute BE is for the Smart-ups...i did not know this...thks

-The Model of the PSU in the PL370 is 325 Watt PFC -Model:PS-7331-1
-So it seems like I can run the server off the XS model the only concern is the effect the sine wave will have on the PSU and limited Event/Diagnostic logging.

thanks for the info bro, again my goal is to just get more familiar with this and you have already been of a tremendous help.

one last question:even though the combined watts of the PSU in both servers is around 700,,does that mean i have to:
-a:purchase a ups that is rated 700 watt or more?

i thought that there is a difference between the maximum potential draw of each unit(around 400 watts) and the real world requirement (each unit will never draw more than 200 watts) ?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

0 Likes
0
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:38 PM . Last Modified: ‎2024-03-26 01:09 AM

Your next step would be to determine the amount of runtime that you're going to want when the UPS goes to battery for an abnormal power event. The closer you are to full capcity, the less runtime you'll receive. Right now, I'm leaning towards an SUA1500 which is I think off the top of my head, an 865 or 925W UPS. That will cover the initial inrush of the PSU's, then give you a decent amount of runtime while on battery once the PSU's go back down to a normal operating Wattage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore