Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82120members
349628posts

Smart-UPS and charging with a gas generator?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
PaulF1_apc
Cadet
0 Likes
5
616

Smart-UPS and charging with a gas generator?

This was originally posted on APC forums on 10/12/2016


I have owned an APC Smart-700 for many years. I am in the market for a new model.

The problem I have had is the Smart-UPS cannot be charged when power to my house is out and I try to charge the UPS with power from my gas generator - a Honda EM5000SX. The Smart-UPS does not like the input voltage. I have to bypass using my Smart-UPS.

All my radio equipment and house items are happy to run on generator power.

Are there any newer UPS models that will run on most emergency power generators??

PaulF1 

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
616

Re: Smart-UPS and charging with a gas generator?

This reply was originally posted by Allen on APC forums on 10/13/2016


Hello Paul,

Good day to you. May I know how did you confirm that the power from the generator is not accepted by the UPS?

You may want to look at this article discussing the reason why UPS won't operate online:

http://www.apc.com/us/en/faqs/FA158891/

PaulF1_apc
Cadet
0 Likes
0
617

Re: Smart-UPS and charging with a gas generator?

This was originally posted on APC forums on 10/13/2016


When connected to my generator and powering on my UPS, the UPS would always switch immediately to running on batteries mode. I have forgotten which red light was on the UPS front panel. In reading the UPS manual, I see there is a voltage sensitivity adjustment that might be helpful when trying to run on generator power.

I replaced the batteries on the Smart-UPS 700, but I had a new problem. Even with no load, it always lights up "Overload." This UPS is more than 15 years old, so I have decided to scrap it.

I ordered a new APC SMC1000 Smart-UPS. I'll see how it likes my generator.

PaulF1

BillP
Administrator Administrator
Administrator
0 Likes
0
617

Re: Smart-UPS and charging with a gas generator?

This reply was originally posted by David on APC forums on 10/13/2016


I didn't have that bad a problem (Back-UPS XS 1300), just an occasional cut-out (usually when there was a sudden change in the load on the generator).

I put an APC Line-R 1200 AVR unit between my Back-UPS and the generator - that seems to have done the trick.

Tags (1)
UnexpectedBill_apc
Captain
Captain
0 Likes
1
617

Re: Smart-UPS and charging with a gas generator?

This was originally posted on APC forums on 10/13/2016


I was going to suggest lowering the sensitivity on your existing UPS. Even though you've decided to replace it, it's very likely that you'll need to do the same thing on the replacement. And to be honest, even that may not be quite enough if the generator's output waveform is noisy or distorted (as many are at particularly light loads, or when a heavy load first starts up).

The caveat here is that greater distortions and voltage fluctuations may reach your equipment as a result.

You can also adjust the UPS's transfer voltages, in case your generator's output varies more than the default settings will tolerate.

You may also be better served by a true dual-conversion (or "online") style UPS, where the inverter runs at all times and the incoming power is only used to keep the batteries charged. Unfortunately, I don't think APC has any "small" UPSes with this capability.

sbagdon
Ensign
Ensign
0 Likes
0
459

Re: Smart-UPS and charging with a gas generator?

>You may also be better served by a true dual-conversion (or "online") style UPS, where the inverter runs at all times and the incoming power is only used to keep the batteries charged. Unfortunately, I don't think APC has any "small" UPSes with this capability.

 

That was going to be my suggestion, yet as you mention, it's hard to find a double-conversion UPS below 3000kva... and they aren't cheap, usually. We tripped over a SURTD5000RMXLP3U, paying basically weight for it (untested, and they didn't have the plug to test it), and had to replace the batteries (RBC140 with 16 batteries), and the thing is a beast. it'll take just about any crap you send it, convert to DC, then get nice and clean split-phase 240. We don't abuse it, yet it doesn't seem to have any issues with just about any generator brand, including non-inverter generators.