Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Smart-UPS and charging with a gas generator?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Smart-UPS and charging with a gas generator?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

0 Likes
5
7688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

Smart-UPS and charging with a gas generator?

I have owned an APC Smart-700 for many years. I am in the market for a new model.

The problem I have had is the Smart-UPS cannot be charged when power to my house is out and I try to charge the UPS with power from my gas generator - a Honda EM5000SX. The Smart-UPS does not like the input voltage. I have to bypass using my Smart-UPS.

All my radio equipment and house items are happy to run on generator power.

Are there any newer UPS models that will run on most emergency power generators??

PaulF1 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

0 Likes
0
7687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

Hello Paul,

Good day to you. May I know how did you confirm that the power from the generator is not accepted by the UPS?

You may want to look at this article discussing the reason why UPS won't operate online:

http://www.apc.com/us/en/faqs/FA158891/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

0 Likes
0
7688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

When connected to my generator and powering on my UPS, the UPS would always switch immediately to running on batteries mode. I have forgotten which red light was on the UPS front panel. In reading the UPS manual, I see there is a voltage sensitivity adjustment that might be helpful when trying to run on generator power.

I replaced the batteries on the Smart-UPS 700, but I had a new problem. Even with no load, it always lights up "Overload." This UPS is more than 15 years old, so I have decided to scrap it.

I ordered a new APC SMC1000 Smart-UPS. I'll see how it likes my generator.

PaulF1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

0 Likes
0
7688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

I didn't have that bad a problem (Back-UPS XS 1300), just an occasional cut-out (usually when there was a sudden change in the load on the generator).

I put an APC Line-R 1200 AVR unit between my Back-UPS and the generator - that seems to have done the trick.

  • Tags:
  • avr
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

0 Likes
1
7688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:06 AM . Last Modified: ‎2024-03-27 01:14 AM

I was going to suggest lowering the sensitivity on your existing UPS. Even though you've decided to replace it, it's very likely that you'll need to do the same thing on the replacement. And to be honest, even that may not be quite enough if the generator's output waveform is noisy or distorted (as many are at particularly light loads, or when a heavy load first starts up).

The caveat here is that greater distortions and voltage fluctuations may reach your equipment as a result.

You can also adjust the UPS's transfer voltages, in case your generator's output varies more than the default settings will tolerate.

You may also be better served by a true dual-conversion (or "online") style UPS, where the inverter runs at all times and the incoming power is only used to keep the batteries charged. Unfortunately, I don't think APC has any "small" UPSes with this capability.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbagdon
sbagdon
Contributor

Posted: ‎2021-09-10 07:23 PM

In response to Anonymous user
0 Likes
0
7530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-10 07:23 PM

>You may also be better served by a true dual-conversion (or "online") style UPS, where the inverter runs at all times and the incoming power is only used to keep the batteries charged. Unfortunately, I don't think APC has any "small" UPSes with this capability.

 

That was going to be my suggestion, yet as you mention, it's hard to find a double-conversion UPS below 3000kva... and they aren't cheap, usually. We tripped over a SURTD5000RMXLP3U, paying basically weight for it (untested, and they didn't have the plug to test it), and had to replace the batteries (RBC140 with 16 batteries), and the thing is a beast. it'll take just about any crap you send it, convert to DC, then get nice and clean split-phase 240. We don't abuse it, yet it doesn't seem to have any issues with just about any generator brand, including non-inverter generators.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore