Smart-UPS SRT 3000 web-interface shows critical alarm (Battery needs replacement) but Battery System Status shows everything ok

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS SRT 3000 web-interface shows critical alarm (Battery needs replacement) but Battery System Status shows everything ...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Sugus
Sugus
Cadet

Posted: ‎2024-04-17 05:04 AM

0 Likes
3
3198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-17 05:04 AM

Smart-UPS SRT 3000 web-interface shows critical alarm (Battery needs replacement) but Battery System Status shows everything ok

Our Client has a Smart-UPS SRT 3000. The web-interface shows a critical alarm in the top right corner, that the battery needs replacement (the last battery replacement apparently was 14 months ago). But when i check under Status -> Battery System ; the internal pack shows health and status as OK. I did a Self-Test as well as a Calibration which both passed. But the critical alarm in the top right corner is still showing.

Are there some specific steps i have to do to reset the critical alarms present or is there a possibility that something is wrong with the battery / UPS?

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-23 09:02 AM

In response to Sugus
0 Likes
0
3115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-23 09:02 AM

A few questions and possible answers below.

 

Cartridge: Have you physically inspected and verified the battery cartridge is fine while taking the proper measurements?

 

Do you have a spare to insert to see how the unit behaves? If the message clears upon inserting a brand new cartridge the prior cartridge was faulty / End of Life.

 

Reboot: Have you tried to reboot the UPS to see if the fault clears?

 

Brain Dead: This procedure will clear possible errors in the units MCU. This will NOT resolve any battery issues that may be present such as an expired cartridge etc.

 

Disconnect all loads. Remove AC Mains from the wall outlet. Disconnect the battery cartridge. Press and hold the power button until you hear a click / beep.

 

You may not hear anything at all either.

 

Reconnect everything (except) the battery cartridge and loads. Power on the unit and let the system complete the POST.

 

The system will obviously declare a fault about a missing (disconnected) battery cartridge. This message should be present if not - Stop!

 

If the message is present insert the battery cartridge. The system may ask you to confirm this is a new battery cartridge. You can take a gamble and say no. But you can also say yes and the system will reset the internal counters and charging parameters.

 

Once that is done initiate a manual Self Test using the LCD. Do not use the NMC to initiate the Self Test!

 

Report back what happens and your observations. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-17 07:34 AM

0 Likes
0
3178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-17 07:34 AM

When the alarm is presented there should be several options. One is to clear the active fault vs just silencing the fault.

 

You’ll obviously select the other option vs the one you chose before. 

In the worst case scenario you can change the battery installation date by one month either via the LCD or NMC in the field you showed in your screen capture. 

NOTE: You’ll really want to confirm the battery’s cartridge was indeed physically changed out. As many IT professionals simply reset the counter as seen in your image capture to save finances / time! 🤦‍♂️👎

 

The battery cartridge has a production serial number. Unless the cells were replaced instead of replacing the entire cartridge that is the actual build date.

 

Let me know what you find and the next steps you take to resolve the issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Sugus
Sugus
Cadet

Posted: ‎2024-04-23 08:13 AM

0 Likes
1
3120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-23 08:13 AM

I don't see any options to clear or silence active faults. Where would i find those? (or is there a telnet command for that. couldn't find anything so far)

Tried to change the battery installation date like you suggested, but that didn't make a difference.

I can't be 100% sure that the battery was changed, but i see a log-entry that the battery was disconnected at the same date as the battery installation date. so i guess it really was replaced.

 

thank you for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-23 09:02 AM

In response to Sugus
0 Likes
0
3116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-23 09:02 AM

A few questions and possible answers below.

 

Cartridge: Have you physically inspected and verified the battery cartridge is fine while taking the proper measurements?

 

Do you have a spare to insert to see how the unit behaves? If the message clears upon inserting a brand new cartridge the prior cartridge was faulty / End of Life.

 

Reboot: Have you tried to reboot the UPS to see if the fault clears?

 

Brain Dead: This procedure will clear possible errors in the units MCU. This will NOT resolve any battery issues that may be present such as an expired cartridge etc.

 

Disconnect all loads. Remove AC Mains from the wall outlet. Disconnect the battery cartridge. Press and hold the power button until you hear a click / beep.

 

You may not hear anything at all either.

 

Reconnect everything (except) the battery cartridge and loads. Power on the unit and let the system complete the POST.

 

The system will obviously declare a fault about a missing (disconnected) battery cartridge. This message should be present if not - Stop!

 

If the message is present insert the battery cartridge. The system may ask you to confirm this is a new battery cartridge. You can take a gamble and say no. But you can also say yes and the system will reset the internal counters and charging parameters.

 

Once that is done initiate a manual Self Test using the LCD. Do not use the NMC to initiate the Self Test!

 

Report back what happens and your observations. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore