Smart-UPS 500 (SCL500RM1UNC) no power on switched outlet groups

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS 500 (SCL500RM1UNC) no power on switched outlet groups
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
APC EASY UPS BV 500VA, AVR, Universal Outlet, 230V

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-08 10:48 AM

0 Likes
9
4250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-08 10:48 AM

Smart-UPS 500 (SCL500RM1UNC) no power on switched outlet groups

Hi,

I have a new Smart-UPS 500 (SCL500RM1UNC) and I'm unable to get power on

Group 1: Outlet Group 1 On
Group 2: Outlet Group 2 On

They are both switched on and there is no power on the outlets. Same when I switch them off.
The battery is fully charged and the UPS is in normal state and connected to the grid.

With my other UPS'es (other models) this works perfect.


The unswitched group has power and works perfect.

Main: Unswitched Group On


Is this normal? I'm trying to find out if this one is defective or if I'm missing something.

Kind Regards
Fred.

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2022-01-12 01:04 PM

0 Likes
7
4226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-12 01:04 PM

@Fred. 

 

If the outlets show that they are on and no AC is available you should contact local Schneider Electric  technical support for assistance.

 

Local support contact information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

You may need to change the region in the upper left of the contact us web page. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-13 02:21 AM

In response to BillP
0 Likes
6
4223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-13 02:21 AM

Hi Bill,

Thanks for your reply.

I contacted support and I have done that before with another issue but I usually get no reply or sometimes months later...
APC Support really sucks here that's why I tried it here.

Kind Regards
Fred.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2022-01-14 10:02 AM

In response to Fred.
0 Likes
5
4212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-14 10:02 AM

@Fred. 

 

I am sorry you are experiencing this inconvenience. 

 

  1. Have you verified the battery is connected correctly?
  2. Is the unit connected to the local network, and if so, does the network card report the UPS on and output on?
  3. Is the UPS connected to the SmartConnect portal, has it been registered, and what is the product ID?
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-15 01:17 PM

In response to BillP
0 Likes
4
4198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-15 01:17 PM

Hi Bill,

 

See the inline reply

Have you verified the battery is connected correctly?
Yes, Visually checked it and it reports healthy.

Battery Status
State of Charge
100.0 %
Battery Voltage
15.7  VDC
Health

 OK

UPS Input

Input Voltage
228.1  VAC @  50.0  Hz


Is the unit connected to the local network, and if so, does the network card report the UPS on and output on?

Yes

UPS Output
Output Voltage
229.9  VAC @  50.0  Hz
Load Current
0.0  Amps
Output VA
0.0 %
Output Watts
0.0 %
Output Energy Usage
17.38 kWh

Outlet Group Status
Group State
Main: Unswitched Group On
Group 1: Outlet Group 1 On
Group 2: Outlet Group 2 On

Only the unswitched group has power.

Is the UPS connected to the SmartConnect portal, has it been registered, and what is the product ID?
No it's not connected to the smartportal and not registered.


About UPS
Model
Smart-UPS 500
SKU
SCL500RM1UNC
Serial Number
5S2112T52850
Firmware Revision
UPS 02.5 (ID1029)
Manufacture Date
03/28/2021
Apparent Power Rating
500  VA
Real Power Rating
400  W
Battery SKU
APCRBC167-LI

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-18 12:46 AM

In response to Fred.
0 Likes
0
4172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-18 12:46 AM

I called support again today and was promised they are going to take up the case.
Let's see if I hear something back from them in the next days. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2022-01-18 12:41 PM

In response to Fred.
0 Likes
2
4165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-18 12:41 PM

Hi,

 

The SCL5000RM1UNC is designed for 

Input frequency
47 - 63 Hz
Input voltage range for main operations
92 - 139V
 
If your input voltage is 228.1 the UPS will not work. If you are located in an area the normal AC is 50 Hz, 230V you should be using a SCL500RMi1UNC
 
https://www.se.com/ww/en/product/SCL500RMI1UNC/apc-smartups-c-lithium-ion-short-depth-500va-230v-wit...
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-19 01:41 AM

In response to BillP
0 Likes
1
4161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-19 01:41 AM

Hi Bill,

It's a SCL500RMi1UNC. But there is something wrong with it.
I send them logs and screenshots.
They agreed to swap it.

Just waiting to hear when they want to do the swap now.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-01-19 01:52 AM

In response to Fred.
0 Likes
0
4159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-01-19 01:52 AM

I see what's going on now.

The box and the back of the device says it's a SCL500RMi1UNC but the SKU says SCL500RM1UNC

I guess this device was made on a Monday morning ๐Ÿ˜›

Also the Quality Assurance test is not signed. but passed. And it reports SCL500RMi1UNC

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fred.
Crewman Fred.
Crewman

Posted: โ€Ž2022-02-01 09:31 AM

0 Likes
0
4070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-02-01 09:31 AM

I received a new UPS today same model but this one is working perfectly.

Thanks everyone ๐Ÿ™‚

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore