Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Serious Problems with (sort of) new XS1300

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Serious Problems with (sort of) new XS1300
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

0 Likes
3
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

Serious Problems with (sort of) new XS1300

I'm the "tech guy" for a small business office. "The Boss" bought an XS1300 from Best Buy 6 months ago and it sat new in the box until last week.

I installed it on their server and right from the start there were problems. The batteries seemed to not be able to hold a charge, and Powerchute reported there was always "less than a minute" even with the wattage draw was 0 watts.

I called APC Tech Support (I have a case number somewhere) and told him about the 6 months between purchase and use and he said the batteries were probably bad. So today I bought two more batteries, removed the old ones and rebuilt the battery pack and it behaves even worse now than it did before I started.

I spent a week with the old batteries "stretching" them, by draining them completely, then charging them completely i.e. "deep cycling" and after a week I was able to get the batteries to output 75 watts for about 17 minutes. This was an improvement from the 3 that I was getting in the beginning. Despite this "success", both the battery and the APC software claimed there was never any power available, which was somewhat true but not completely.

I've been reading online about something called "calibration" and am wondering is this is the problem.

Any help ?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

I'm the "tech guy" for a small business office. "The Boss" bought an XS1300 from Best Buy 6 months ago and it sat new in the box until last week.

I installed it on their server and right from the start there were problems. The batteries seemed to not be able to hold a charge, and Powerchute reported there was always "less than a minute" even with the wattage draw was 0 watts.

I called APC Tech Support (I have a case number somewhere) and told him about the 6 months between purchase and use and he said the batteries were probably bad. So today I bought two more batteries, removed the old ones and rebuilt the battery pack and it behaves even worse now than it did before I started.

I spent a week with the old batteries "stretching" them, by draining them completely, then charging them completely i.e. "deep cycling" and after a week I was able to get the batteries to output 75 watts for about 17 minutes. This was an improvement from the 3 that I was getting in the beginning. Despite this "success", both the battery and the APC software claimed there was never any power available, which was somewhat true but not completely.

I've been reading online about something called "calibration" and am wondering is this is the problem.

Any help ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

Thanks JonPro. I'll do this today and report results.

Are these directions published anywhere ? How would a person in my situation know how to do this procedure ?

I've done something similar to this, but did not load the battery down to 35%.

Would this need to be done on a battery back-up that has brand-new batteries ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

You are welcome Jonny.

We have an APC Knowledge Base article that shows these steps -> [APC KBase 1497|http://nam-en.apc.com/app/answers/detail/a_id/1497/kw/flashing%20battery]. On the knowledge base it talks about the APC Smart-UPS units. It is best to do this steps on UPSs that has a new battery, there are some cases wherein we also do this when the battery is within a year old.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

0 Likes
0
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:18 AM . Last Modified: ‎2024-03-22 12:54 AM

I'm the "tech guy" for a small business office. "The Boss" bought an XS1300 from Best Buy 6 months ago and it sat new in the box until last week.

I installed it on their server and right from the start there were problems. The batteries seemed to not be able to hold a charge, and Powerchute reported there was always "less than a minute" even with the wattage draw was 0 watts.

I called APC Tech Support (I have a case number somewhere) and told him about the 6 months between purchase and use and he said the batteries were probably bad. So today I bought two more batteries, removed the old ones and rebuilt the battery pack and it behaves even worse now than it did before I started.

I spent a week with the old batteries "stretching" them, by draining them completely, then charging them completely i.e. "deep cycling" and after a week I was able to get the batteries to output 75 watts for about 17 minutes. This was an improvement from the 3 that I was getting in the beginning. Despite this "success", both the battery and the APC software claimed there was never any power available, which was somewhat true but not completely.

I've been reading online about something called "calibration" and am wondering is this is the problem.

Any help ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore