Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sensitivity settings on Back-UPS ES Models

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Sensitivity settings on Back-UPS ES Models
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
4
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

Sensitivity settings on Back-UPS ES Models

On the APC Knowledge Base you can find a document showing the voltage disturbances that can make a Smart-UPS transfer to battery power and what kind of voltage disturbance each level of sensitivity can detect. The document I'm talking about is this:

http://lam-en.apc.com/app/answers/detail/a_id/62/kw/Sensitivity/session/L3RpbWUvMTI4MTc1MzIxMS9zaWQv...

What I want to know is if the sensitivity setting for the Back-UPS line works the same way as on the Smart-UPS line. Does the Back-UPS line detects the same kind of voltage disturbance as the Smart-UPS line?

Thanks!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
0
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

On the APC Knowledge Base you can find a document showing the voltage disturbances that can make a Smart-UPS transfer to battery power and what kind of voltage disturbance each level of sensitivity can detect. The document I'm talking about is this:

http://lam-en.apc.com/app/answers/detail/a_id/62/kw/Sensitivity/session/L3RpbWUvMTI4MTc1MzIxMS9zaWQv...

What I want to know is if the sensitivity setting for the Back-UPS line works the same way as on the Smart-UPS line. Does the Back-UPS line detects the same kind of voltage disturbance as the Smart-UPS line?

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
voidstar_apc
Contributor

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
0
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

>
I asked this because the Smart-UPS line look for THD - Total Harmonic Distortion - and since it is a known subject that a stepped sinewaves contains a good amount of harmonic distortion, I was thinking it wouldn't be very clever for the Back-UPS line to look for harmonic distortion, unless the THD of a Back-UPS unit is lower than the level detected on the AC Sinewave prior to transferring to battery power.
>

For a single Back-UPS unit, the criteria for the AC line being good seems unrelated to the output waveform. Of course if you plug one Back-UPS into another, I'd expect them both to go on battery when AC is bad.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

My point is, if the Back-UPS transfers to battery because of detected harmonic distortion on the AC sinewave, it won't do any usefull work since the output wave of the Back-UPS models is full of harmonic distortion as well, I just don't know how much. For the Smart-UPS unit APC says the THD is lower than 5%, which is better than the AC sinewave of many facilities.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

>
My point is, if the Back-UPS transfers to battery because of detected harmonic distortion on the AC sinewave, it won't do any usefull work since the output wave of the Back-UPS models is full of harmonic distortion as well, I just don't know how much. For the Smart-UPS unit APC says the THD is lower than 5%, which is better than the AC sinewave of many facilities.
>

Ah, I think I see what you're saying: If the purpose is to protect the attached devices from harmonic distortion, then transferring to battery and generating a psuedo-sinewave when such distortion is detected defeats the purpose.

I think the purpose is to detect power failures before the voltage dips too low. In the time domain, such disturbances are sudden deviations from a perfect sine wave. In the frequency domain, that shows up as harmonic distortion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

0 Likes
0
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:00 AM . Last Modified: ‎2024-03-22 01:02 AM

On the APC Knowledge Base you can find a document showing the voltage disturbances that can make a Smart-UPS transfer to battery power and what kind of voltage disturbance each level of sensitivity can detect. The document I'm talking about is this:

http://lam-en.apc.com/app/answers/detail/a_id/62/kw/Sensitivity/session/L3RpbWUvMTI4MTc1MzIxMS9zaWQv...

What I want to know is if the sensitivity setting for the Back-UPS line works the same way as on the Smart-UPS line. Does the Back-UPS line detects the same kind of voltage disturbance as the Smart-UPS line?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore