Second "Replace Battery" problem in 7 months

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Second "Replace Battery" problem in 7 months
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

0 Likes
3
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

Second "Replace Battery" problem in 7 months

I just got a notification for the second time that my battery should be replaced.  I replaced the battery in March of this year, my unit is/was still under warranty.  Before I called customer support again I wanted to see if anyone had any ideas why this is happening?

The first time my battery "died" I had bought my UPS 6-8 months prior but never got around to setting it up, so the battery sat.  When APC warrantied me a new battery they told me to not let the battery sit for 6+ months at a time.  I've been using the new battery since I received it.

For the past month or two I've only a couple devices running off of the battery backup, it's at 84W, 9% load right now.  I first got the notification a couple of weeks ago about the battery.

Should my whole unit be replaced?  It's a BR1500G.

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

What if you do another self test on the UPS? Does the alarm clear?

The UPS self test compares the voltage drop on the battery with your load against a "table" it stores internally that defines what the normal tolerance for the voltage drop would be. Sometimes you can see it fail once for one reason or another but then it will pass a subsequent test.

Like, maybe it did a self test right after you did have a quick power event so the battery was a little discharged, just as an example of when you could see the behavior.

I don't think a unit replacement would help here. If anything, it is likely a blip in the battery voltage drop that triggered it or the battery indeed has failed prematurely. Since you had this issue before is why I asked those other questions to see if something in the environment is contributing to a premature failure.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

Hello,

Does the UPS go onto battery operation frequently? Where is the UPS located (as in the ambient environment)? There are several factors that contribute to battery life such as over all usage, manufacturing defect, ambient temperature, environment, etc.

We warranty this unit and its battery for three years though at least but you could consider any of those factors I mentioned to see if anything sticks out to you. (There is some general information on temperature here -> http://www.schneider-electric.com/support/index?page=content&country=US〈=en&locale=en_US&id=FA156516)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

Thanks for the reply, no it rarely goes onto battery operation.  I have very reliable power in New Jersey.  The temperature was never above 70 degrees Fahrenheit and has been down around 65 recently.  It has plenty of ventilation around it as well. I'd rather not warrant they whole unit because I don't really want a refurbished one, but maybe it has to be done.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

0 Likes
0
1263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:07 PM . Last Modified: ‎2024-03-20 03:17 AM

What if you do another self test on the UPS? Does the alarm clear?

The UPS self test compares the voltage drop on the battery with your load against a "table" it stores internally that defines what the normal tolerance for the voltage drop would be. Sometimes you can see it fail once for one reason or another but then it will pass a subsequent test.

Like, maybe it did a self test right after you did have a quick power event so the battery was a little discharged, just as an example of when you could see the behavior.

I don't think a unit replacement would help here. If anything, it is likely a blip in the battery voltage drop that triggered it or the battery indeed has failed prematurely. Since you had this issue before is why I asked those other questions to see if something in the environment is contributing to a premature failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore