SYS FAULT CONDITIONUTILITY PHASE FAULT

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
michaelabend_apc
Crewman
Crewman
0 Likes
3
162

SYS FAULT CONDITIONUTILITY PHASE FAULT

This was originally posted on APC forums on 4/29/2018


I have a newly installed UTS10BI and aside from testing it has not been used.  a few weeks after installing (by a licensed electrician) i went to swap out a GFCI outlet on one of the circuits the UTC is connected to.  I initially connected the wires to the wrong contacts - i should be sure to have my reading glasses on when i do this stuff! - and seemingly as a result the UTC is now flashing all lights and shows the above message.  i have since corrected the error (outlet works fine) and it continues to show this message and lights continue to flash. i cannot believe a small error like that did some sort of damage to the unit since it didnt even set off the circuit breaker on the panel. i knew i had made an error because the reset button wouldn't engage on the outlet.

any guidance would be appreciated.  i have not tried to turn off the main breaker but wonder if that is all it will take.

thanks in advance for any help!


Accepted Solutions
michaelabend_apc
Crewman
Crewman
0 Likes
0
162

Re: SYS FAULT CONDITIONUTILITY PHASE FAULT

This was originally posted on APC forums on 5/2/2018


the utc went back to normal when i turned off hte main and turned it back on, simple solution!

thanks, wayne

See Answer In Context

3 Replies 3
wayne_i_apc
Lieutenant
Lieutenant
0 Likes
0
162

Re: SYS FAULT CONDITIONUTILITY PHASE FAULT

This was originally posted on APC forums on 4/29/2018


Hi Michael,

I would suggest turning off the circuit breaker in your main panel that feeds the UTS circuits 9 / 10 for a few seconds. If you do NOT have a UPS connected to the "UPS Inlet" connector this will reset the UTS, which I believe monitors circuits 9 & 10 to detect the "Utility Phase Fault" that is being reported. If you do have a UPS connected, you may need to turn it off while the 9 / 10 circuit breaker is turned off to accomplish the reset.

From your description of the incident that caused this problem I can't understand what really happened, or venture a guess as to why it caused the problem...

Please post your progress in solving this problem.

Wayne

michaelabend_apc
Crewman
Crewman
0 Likes
0
162

Re: SYS FAULT CONDITIONUTILITY PHASE FAULT

This was originally posted on APC forums on 4/30/2018


disconnecting the UTS from the system didn't do a thing, nor did resetting the circuit.  i am going to reach out ot the electrician who installed it.  thanks anyway.

michaelabend_apc
Crewman
Crewman
0 Likes
0
163

Re: SYS FAULT CONDITIONUTILITY PHASE FAULT

This was originally posted on APC forums on 5/2/2018


the utc went back to normal when i turned off hte main and turned it back on, simple solution!