We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on
Cloud Connected vs On-Premise Services. Your feedback can
help us shape the future of services.
Learn more about the survey
or
Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
I have a Smart-UPS with a sticker on it that says the model is a SUV650. My question is this... on-battery power I am seeing about 85volts with a standard Fluke 77 multimeter. Is this normal relative to the output waveform this particular unit produces?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
This is normal. Please read the document at the link below for an explanation
http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/step approx
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:27 AM . Last Modified: 2024-03-21 04:54 AM
Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of