SUM1500RMXL2U - Anomalous State

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SUM1500RMXL2U - Anomalous State
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All
Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
kylebroflovski
kylebroflovski
Cadet

Posted: ‎2023-11-07 07:57 PM

0 Likes
1
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-07 07:57 PM

SUM1500RMXL2U - Anomalous State

Greetings,

 

I would appreciate any help or additional insight.

 

This computing site uses 1 APC Smart-UPS SUM1500RMXL2U (www.apc.com/us/en/product/SUM1500RMXL2U/). For this model, the LED panel has 4 colummns. Left-to-right and top-to-bottom, the columns are:

 

1: Load
2: AVR Trim/Boost,    On Line,       Bypass
3: Overload,          On Battery,    Replace Battery
4: Battery Charge

 

Some indeterminate event occurred. What specifically, is unbeknownst to me. The first time any indication that a negative event occurred is that the next self test resulted in a failure, and the following LED configuration:

 

1: All 5 flashing
2: AVR Trim/Boost flashing
   On Line flashing
   Bypass steady on
3 & 4: Off

 

There is the low pitch sound of the power module disconnecting the battery and connecting the receptacles directly to line (a single "thump"). There is no audible tone.

 

While this is an unrecognized LED configuration, the first suspicion is to replace the RBC43 SSLA battery. The UPS is disconnected from line. That battery during which this event first occurred is replaced with a new one. The UPS is re-connected to line. Following is what is then observed:

 

* If the UPS is powered on without being connected to the battery, it completes the portions of the self test that excludes the battery, and both the Replace Battery LED and the short intermittent audible tone are enabled. This is expected normal behavior.

 

  Upon connection of the new battery, i.e. it is as if the battery is hot-swapped, the Replace Battery LED and the short intermittent audible tone are disabled. This is expected normal behavior.

 

  The UPS behaves and runs as usual, until the next self test. When the self test occurs, the above behavior and LED configuration, which caused me to initially suspect the former battery, returns.

 

* If the UPS is powered on being connected to the battery, during the self test, the above behavior and LED configuration occur immediately after.

 

Again, I would appreciate any help or additional insight as to what is going on with the UPS.

 

Thanks to everyone in advance.

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
  • RBC43
  • smart-ups
  • SUM1500RMXL2U
  • unknown anomalous state
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Spock Teken
Spock

Posted: ‎2024-02-07 11:15 AM

0 Likes
0
653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-07 11:15 AM

If Power Chute software is loaded and in use I would check the logs to see what error codes have been captured. Once known reach out to APC Support for insight and feedback as to possible next steps. Once you have obtained any logged information you can try the following.

 

1. Using Power Chute, default the unit to factory settings.

 

2. Brain Dead: Unplug AC Mains from the wall. Disconnect the battery from the UPS. Press and hold the power button until you hear a click / beep. Reconnect the battery cartridge and AC Mains to the UPS.

 

3. Battery Calibration: Using Power Chute software initiate a battery calibration on the new battery. Insure there is at least 30% connected load to the UPS. Once that process has completed let the UPS recharge the new cells and report back if the runtime falls within the expected duration.

 

4. Self Test: Initiate the self test via the Power Chute software and report back success / failure.

 

Cheers! 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of