Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SUA1000 Blinking "Replace Battery" and Beeping Every 2 Seconds

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SUA1000 Blinking "Replace Battery" and Beeping Every 2 Seconds
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
9
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

SUA1000 Blinking "Replace Battery" and Beeping Every 2 Seconds

I actually just got this UPS free from someone on Craigslist who said that it just started doing this. As far as I know the batteries have never been replaced, but I want to make sure this is a battery issue and not something with the unit itself. I've tested both batteries and they each read 13.3 volts, as well as the unit. I just want to make sure that I'm buying batteries as long as the UPS is still in good order.

If I unplug it, it will not discharge to any devices plugged into it, but if I push the Test button it will show a charge of 1/5. This is weird...

Message was edited by: Alpha_Link

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

it does sound like old batteries based on what you said. i agree with barry on this one as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

Hi Matt,

The fault that your UPS has encountered is what do we call as "disconnected battery". Although the battery is connected/attached, the unit fails to detect it. Normal troubleshooting that we recommend are reseating the battery connector/wires, trying a good working batteries and at the back of your unit there is a black plastic plug which we call quick battery connector. Make sure that the connector is seated properly and doesn't get loose.

There's a chance that buying a battery would make it work as it should but sometimes that doesn't fix the problem if it is the charging mechanism that failed. What's the serial number of the unit, let's see how old the UPS is.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

The serial number is: AS0442110476

I've tried reseating the connectors, triple checking that they are tight. The battery connector on the back is seated properly as well. Like I said, it appears that the UPS is getting a charge from the battery, as it's showing a charge on the LED meter when unplugged, but it won't discharge to anything plugged in to the outlets in the back of the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

Matt,

Based from the serial number, your unit was manufactured on the 42nd week of 2004. From your findings and troubleshooting, it would be best to replace the UPS itself if possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

hmm, do you have a clue on what the problem could possibly be? I really don't want to get rid of something I got for free if there might be a chance of fixing it.

Message was edited by: Alpha_Link

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-21 05:10 AM

when you say it won't discharge to any of the load when you put the UPS on battery, what specifically happens? UPS turns off or does it keep going, thinking its working? i am wondering if the batteries are just the original and indicate charged but cannot support a load.

depending on your answer here, we can make a recommendation again for batteries or different UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

If I unplug the UPS from the wall, the UPS shuts off. However, while it's unplugged, I can push the Test button and the LED meter will appear to show a charge of 1/5. You would think that the batteries would be drained if they are not discharging, but the UPS is getting some kind of power from them. And I measured around 13 volts on each of them.

From what I know the batteries are original, which was the reason why the guy who gave them to me said he was getting rid it (and why it's acting this way).

Message was edited by: Alpha_Link

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

A battery showing 13 volts does not necessarily mean it is any good. When you put a load on the battery, if bad, it can immediately drop to an unacceptable voltage level.

If you do not have real testing equipment, connect the battery to a load.. say an old headlight in your garage.. if it lights at all, now test the battery voltage.

You should also check the ups charging voltage. just connect your volt meter to the wires that connect to the battery (with the battery disconnected).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

Hmm, could be. I did check the wires on the UPS and they were giving out 13 volts. I can bring the batteries to my local auto parts store which I know they have equipment to test out the batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:04 AM . Last Modified: ‎2024-03-21 05:10 AM

it does sound like old batteries based on what you said. i agree with barry on this one as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore