SUA 2200UXI - all 6 LEDs flashing

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SUA 2200UXI - all 6 LEDs flashing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:44 AM

0 Likes
5
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:44 AM

SUA 2200UXI - all 6 LEDs flashing

Hi,

I got a SUA2200UXI two years back. Exactly after 1 year the problem first occurred and I got a replacement. Now exactly after one more year, the problem has again started few days back.


Symptoms:
While in operation, suddenly the 6 LEDs start flashing (AVR Trim,ON Line,AVR Boost,Overload,On Battery and Replace Battery) and the UPS cuts off power to all peripherals.
If I restart the UPS, it does work for a while but again the problem arises after a few minutes.

Things I have tried:
Tried to change the sensitivity setting behind the UPS, but the problem occurs at all 3 sensitivity settings.

I'm guessing the prob is the same as in this thread:
http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/6602/smart-ups-sua-1500i-with...

I'm still under the 2 year warranty period and might be lucky to get a replacement again. But worried, what I would do once warranty runs out.

Is this due to a malfunctioning relay? Here is a video of the prob:
http://www.youtube.com/watch?v=jtvaNu8RjcM

Please advise.

Thanks,
Pappu

Message was edited by: pappusmailbox

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

You are very much welcome.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:44 AM

0 Likes
0
698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:44 AM

unfortunately, this indicates an AVR relay weld and generally is not fixable. is automatic voltage regulation constantly in use?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

Not constantly...but definitely a few hours everyday in the morning and at night.
(Load is minimal, approx 400W)

I gathered some more info about this particular problem from here:
http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/2824/apc-be550g-battery-back...

But what I'm tensed about is that you are saying its not fixable. For now, I'll probably get a replacement. But later on, if this happens again, can't I get the faulty relay replaced with a new one with identical specifications....will that work? (a friend of mine says its not a very expensive component)

What do you say?

Message was edited by: pappusmailbox

Message was edited by: pappusmailbox

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

Unfortunately APC doesn't sell relay's. If the unit is out of warranty and you want to have it repaired, you can contact our authorized service center - Coastal Business Machines.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

Thanks for all the help folks 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

You are very much welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of