SU1400 Not Charging?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SU1400 Not Charging?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
3
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

SU1400 Not Charging?

Hiya,

I've got an old APC Smart-UPS 1400 that's been running well for the last 8 years! 🙂

The batteries overheated yesterday and I noticed the 5 battery level LED's were all flashing. I I removed the battery pack, which had also slightly leaked - I assume that's normal for something that's only supposed to last 5 years! 🙂

I've replaced the battery with a brand new set, but have the same problem with the flashing LEDs.

PowerChute shows the battery status as GOOD, but the screen shows;
Battery Capacity: 100%
Battery Status: Discharged
Battery Voltage: 27.87 VDC
Runtime Remaining: 0 min.
UPS Load: 28%
Temperature: 29.7^o^C

It's been plugged in for a few hours now, but it's still showing as discharged. How can the battery capacity be 100% with a runtime of 0 minutes? I ran a sef test on low load and it passed.

If this a charging issue or an incompatability between PowerChute Basic Business Edition and an old UPS?

Any advice, that's cheap to implement(!), would be much appreciated.

Chat soon.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

Hiya,

I didn't get as far as running the manual runtime calibration - I didn't have an easy 30% load that wasn't critical 🙂

I was talking to APC about the Calibration Key and they sent me the manual steps to perform the same function. Hyperterminal and change the Battery Constant. Seems the constant value is different for each model of UPS, so I'll not publish the value here, but a value of 0x14 is bad, and one much bigger is better! 🙂

I've now donce a runtime calibration via Powerchute and all seems to be functioning correctly!

Thanks for the advice, and I've learnt a lot about the CalKey stuff.

Chat soon.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

The runtime probably dropped unacceptably low before your battery completely failed. You should do a runtime test annually and replace the battery if the runtime at current load is no longer acceptable.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

I'd recommend 2 things. First is going to be a manual runtime calibration. This is outlined in the document below and is just to make sure you're going to get the expected runtime from the batteries.

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1497

Once you realize the you are getting the runtime, put a call into tech support at 800-890-4272. They can get you out a calibration key to to recalibrate the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:51 PM . Last Modified: ‎2024-03-26 12:57 AM

Hiya,

I didn't get as far as running the manual runtime calibration - I didn't have an easy 30% load that wasn't critical 🙂

I was talking to APC about the Calibration Key and they sent me the manual steps to perform the same function. Hyperterminal and change the Battery Constant. Seems the constant value is different for each model of UPS, so I'll not publish the value here, but a value of 0x14 is bad, and one much bigger is better! 🙂

I've now donce a runtime calibration via Powerchute and all seems to be functioning correctly!

Thanks for the advice, and I've learnt a lot about the CalKey stuff.

Chat soon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore