SRT2200 / SRT3000 Configuring Outlet Group to switch on after mains input present

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
Rooster_apc
Ensign
Ensign
0 Likes
1
203

SRT2200 / SRT3000 Configuring Outlet Group to switch on after mains input present

This was originally posted on APC forums on 4/7/2017


Hi. we have a number of SRT2200 and SRT3000 UPS' all fitted with NMC2 Management Cards. I need the Output Groups to automatically enable once mains input is applied. I've been through all the options in the Management Card (V6.4) but cannot get them to do this. Am I missing something? Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
203

Re: SRT2200 / SRT3000 Configuring Outlet Group to switch on after mains input present

This reply was originally posted by Vinay on APC forums on 4/7/2017


Hi Richard,

Outlet groups are turned on automatically until and unless they are configured to be in off state. Make sure the outlet groups are turned on and the "stay off after power returns" options is unchecked in the outlet group configuration section.

See Answer In Context

Attachments
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
204

Re: SRT2200 / SRT3000 Configuring Outlet Group to switch on after mains input present

This reply was originally posted by Vinay on APC forums on 4/7/2017


Hi Richard,

Outlet groups are turned on automatically until and unless they are configured to be in off state. Make sure the outlet groups are turned on and the "stay off after power returns" options is unchecked in the outlet group configuration section.

Attachments