SMX1500RM BATTERY ISSUE
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-2105:12 AM
Given you haven’t provided any context about the history of this unit and the battery cartridge.
Here are some basic questions to answer and consider:
Serial Number: What is the serial number?
Battery: How old is the battery cartridge?!? The service life is stated as 2-5 years based on usage, temperature, and environmental conditions.
Voltage: What does the system indicate the float voltages is while inside the unit?!? What is the float voltage when the cartridge is removed and allowed to sit for 72 hours?!?
Self Test: What are the results of the Self Test?!?
Battery Calibration: The system must have a minimum of 30% attached load. Manually initiate a battery calibration what are the results?!?
Logs: Please upload the Data & Event logs for this system.