Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SMT2200C, Replaced Batteries, Red Flashing Battery Light

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SMT2200C, Replaced Batteries, Red Flashing Battery Light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
o0jeff0o
o0jeff0o
Explorer

Posted: ‎2025-05-27 07:28 AM

0 Likes
6
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-27 07:28 AM

SMT2200C, Replaced Batteries, Red Flashing Battery Light

I have an SMT2200C, purchased in 2018 that’s giving me trouble. 

I let it sit unused for a while, and the batteries died. I replaced all four with the appropriate model, ordered from Amazon and “certified” to work with this device. All four were at close to peak voltage on arrival. Hooked everything up the way I found it. 

Now, I have no Battery related display of any kind (all battery related menus just show null) and the Replace Battery light is flashing red- along with the Connect Battery message showing intermittently. 

every couple hours, I can hear clicking and clacking inside the case- and can also see a “ Battery Replaced?” Message very briefly appear- but before I have time to conform, it goes away. Sometimes it will also briefly show a mid-percentage of battery life, but that also immediately goes away. 

it makes me feel like there’s a loose connection or the plastic housed terminals inside aren’t tightly secured. 

either way, I am unable to do any self tests- the machine doesn’t see a battery and this won’t allow any. I also cannot update FW (I am using really old FW, I’m sure an update would help) because on the online portal you can’t initiate a FW update with the Battery state flag. 

I'm sure this device is out of warranty, but I spent a lot on it, and now more with the battery replacements- I’d really like to get this device back online. I’ve done a ton of troubleshooting found here and various other online sources, and after several frustrating nights I humbly request the experts assistance. 

can anyone point me in the right direction?

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Teken
Champion

Posted: ‎2025-05-27 09:03 AM

0 Likes
0
1864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-27 09:03 AM

Show me a picture of the new cells and the connector along with a photo of the front / back of this unit.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-05-28 03:43 AM

0 Likes
0
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-28 03:43 AM

Well?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

o0jeff0o
o0jeff0o
Explorer

Posted: ‎2025-05-29 09:51 AM

0 Likes
1
1790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-29 09:51 AM

Sorry for the delay, here are the pictures. 

the cells were four individual direct from Amazon and I wired everything exactly as I found it, using pictures of the wiring for reference just to be double sure. 

I tested each unit with a multimeter to verify I didn’t have any dead cells. 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-05-30 02:43 AM

In response to o0jeff0o
0 Likes
0
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-30 02:43 AM

Where’s the rest of the photos??

Reply

Link copied. Please paste this link to share this article on your social media post.

o0jeff0o
o0jeff0o
Explorer

Posted: ‎2025-05-30 05:42 PM

0 Likes
1
1682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-30 05:42 PM

IMG_1523.jpeg

 

IMG_1526.jpeg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-06-02 06:43 AM

In response to o0jeff0o
0 Likes
0
1676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-02 06:43 AM

Complete a brain dead procedure (twice) using the following APC Resource Link for the SMX Series UPS:

 

https://www.apc.com/us/en/faqs/FA156611/

 

Report the behaviour and results here. If the brain dead restores the system to working state - move on.

 

If however, the brain dead procedure does not resolve the issue perform the following and report back the results.

 

Fuse: Remove the fuse and measure the continuity & resistance of the fuse. Insure you wiggle the fuse to validate it’s not cracked. If there is any corrosion remove it and clean.

 

Battery Connected: Measure the battery cartridge voltage (before) it’s connected to the system and document and report back the value. Connect the battery cartridge to the system while it’s connected to AC Mains and powered up.

 

Does the system begin to charge the battery cartridge?!? If so what is the voltage at the battery connector?!?

 

If the battery voltage does not increase report this back.

 

Battery Not Connected: If the battery was being charged by the system proceed with the following:

 

Disconnect the battery cartridge and measure the voltage and document. Allow the battery cartridge to sit for 72 hours and than measure & document the voltage and report back the readings.

 

A brand new and healthy 12 VDC battery that is 100% charged will have a resting voltage depending upon temperature a voltage level of 12.8X ~ 12.9X VDC. It will not drop any voltage during the 72 hour period.

 

Normal voltage drop (self discharge) depending upon environmental temperature is 0.1 VDC.

 

If the fuse and battery check out based on the above reconnect it back to the system. Set your True RMS Multimeter to AC Volts and insert the probes to one of the outputs.

 

Power on the unit and report back the AC Voltage at the outputs the meter is connected to.

 

NOTE: If the system is connected to a computer running Power Chute Software provide the following logs: Event, Data, UPS.

 

On the LCD scroll to the logs and report back the last ten faults / error codes.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore