Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SMART-UPS 1500 doesn't failover to battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SMART-UPS 1500 doesn't failover to battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
152
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
sdmguy
sdmguy
Explorer

Posted: ‎2024-12-09 10:48 AM

0 Likes
3
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-09 10:48 AM

SMART-UPS 1500 doesn't failover to battery

I have had this unit for quite a while. It's been operating as expected until recently. The battery tests fine and the load is well below maximum, but I have a few machines plugged into the unit and when AC power fails, all of the machines plugged in lose power. It's as if the battery is not kicking in at all. Any thoughts? 

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2024-12-16 10:15 PM . Last Modified: ‎2024-12-17 12:57 AM

In response to sdmguy
0 Likes
0
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-16 10:15 PM . Last Modified: ‎2024-12-17 12:57 AM

If the above is true the battery cartridge is ten years old and EOL. The service life is rated for 2-5 years based on usage, temperature, and environmental conditions.

 

A simple test is removing AC power from the wall outlet to see if the unit continues to operate.


Based on your own personal experience it doesn’t and just shuts down. Remove the battery cartridge and measure the voltage depending upon which specific model you have it’s either a 24 / 48 VDC system. 

Both use 12 VDC cells wired in series / parallel. Unplug all the wires connecting the cells and measure the voltage on each individual cell and record / report them here.

 

Come back in 24~72 hours and measure / report back what voltage is seen on each cell. A healthy cell after removing the surface charge will be 12.8 - 12.90 VDC and will drop 0.01 - 0.1 volts.

 

If any cell drops by 0.5 ~ 1.XX VDC just in 72 hours it simply confirms the cell is dead. You can hook up any 12 VDC load to each cell to perform a dynamic test such as a light / fan.

 

You’ll quickly see it won’t power these loads very long if at all. The RBC can be found under the About tab in the LCD. You can purchase a replacement APC RBC cartridge or rebuild the pack yourself using HR rated cells such as CSB which are one of the OEM makers for APC.

 

LOGS: The event / data logs can be viewed from LCD / exported from Power Chute / NMC is present. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Teken
Champion

Posted: ‎2024-12-10 12:04 AM

0 Likes
2
1025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-10 12:04 AM

What do the data & event logs show when you disconnect power from the unit?!?


What is the installation date of the battery cartridge and serial number of the UPS?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

sdmguy
sdmguy
Explorer

Posted: ‎2024-12-16 05:49 PM

In response to Teken
0 Likes
1
969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-16 05:49 PM

Which data and event logs are you referring to? 

Installation date of battery shows as: Sept-2014

Serial # is: 3S1437X06009

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-12-16 10:15 PM . Last Modified: ‎2024-12-17 12:57 AM

In response to sdmguy
0 Likes
0
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-16 10:15 PM . Last Modified: ‎2024-12-17 12:57 AM

If the above is true the battery cartridge is ten years old and EOL. The service life is rated for 2-5 years based on usage, temperature, and environmental conditions.

 

A simple test is removing AC power from the wall outlet to see if the unit continues to operate.


Based on your own personal experience it doesn’t and just shuts down. Remove the battery cartridge and measure the voltage depending upon which specific model you have it’s either a 24 / 48 VDC system. 

Both use 12 VDC cells wired in series / parallel. Unplug all the wires connecting the cells and measure the voltage on each individual cell and record / report them here.

 

Come back in 24~72 hours and measure / report back what voltage is seen on each cell. A healthy cell after removing the surface charge will be 12.8 - 12.90 VDC and will drop 0.01 - 0.1 volts.

 

If any cell drops by 0.5 ~ 1.XX VDC just in 72 hours it simply confirms the cell is dead. You can hook up any 12 VDC load to each cell to perform a dynamic test such as a light / fan.

 

You’ll quickly see it won’t power these loads very long if at all. The RBC can be found under the About tab in the LCD. You can purchase a replacement APC RBC cartridge or rebuild the pack yourself using HR rated cells such as CSB which are one of the OEM makers for APC.

 

LOGS: The event / data logs can be viewed from LCD / exported from Power Chute / NMC is present. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore