SBP5000RMI2U issue

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
blackAces_apc
Commander
Commander
0 Likes
11
217

SBP5000RMI2U issue

This was originally posted on APC forums on 7/27/2010


Hi Guys

Before installation of the bypass panel is there any parameters we need to consider like the orientation of L-L or L-N, L-G from utility and UPS?
Co'z previously from my former company we counter some issue, as normal when the SBP was switch to Normal everything are doing fine but when we switch the SBP to bypass the utility breaker will tripped off and the UPS goes to Battery Mode.
No load connected to UPS and the SBP...,
Is there any issue if the out put of UPS is L-L and the Utility L-G or L-N with regards to the SBP?

Thanks


Accepted Solutions
blackAces_apc
Commander
Commander
0 Likes
0
217

SBP5000RMI2U issue

This was originally posted on APC forums on 7/27/2010


Hi Guys

Before installation of the bypass panel is there any parameters we need to consider like the orientation of L-L or L-N, L-G from utility and UPS?
Co'z previously from my former company we counter some issue, as normal when the SBP was switch to Normal everything are doing fine but when we switch the SBP to bypass the utility breaker will tripped off and the UPS goes to Battery Mode.
No load connected to UPS and the SBP...,
Is there any issue if the out put of UPS is L-L and the Utility L-G or L-N with regards to the SBP?

Thanks

See Answer In Context

11 Replies 11
blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 7/31/2010


yes same configuration that were going to used.

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 7/28/2010


so there is an issue w/ the configuration, co'z our supply line is 220VAC L-L.., so can i say that possible this configuration cause the breaker to Tripped? but the SBP is break-before-make right?

Coz right now we have a client that need SBP for there 3 APC units of SURTD5000XLI, what im worry about is that, what if the breaker will Tripped off again. We can't afford to lose it..

any advice..thanks

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/3/2010


just a few clone server and some router and switches, the breaker rating if I'm not mistaken was 60A.
But the time we switch the SBP to bypass there's no load connected for both UPS and SBP. What we are doing was that time just for a testing only, but i bit surprise when the breaker tripped off.

upsguy_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/3/2010


Did you put the UPS into manual bypass before operating the Bypass switch on the SBP5000RMI2U?

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/4/2010


Nope, just only one of the branch breaker was trip. And that breaker was the supply breaker for the UPS.

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/4/2010


no, we didn't put the UPS into manual bypass when we switch the SBP to Bypass..

upsguy_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/5/2010


Sorry meant to say automatic bypass... Read the upper right hand corner of the install document.

http://www.apcmedia.com/salestools/SCON-7Q3JQ2_R0_EN.pdf

The UPS must be in bypass when rotating the switch. I'd try that then see if your still tripping the upstream breaker.

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/5/2010


on test position it won't trip the breaker only when full bypass position...

blackAces_apc
Commander
Commander
0 Likes
0
217

Re: SBP5000RMI2U issue

This was originally posted on APC forums on 8/5/2010


base from the manual, we have set the ups to automatic bypass right?, its that necessary and why?

BillP
Administrator Administrator
Administrator
0 Likes
0
217

Re: SBP5000RMI2U issue

This reply was originally posted by Matt on APC forums on 8/5/2010


It is necessary to put the double-conversion online UPS into bypass before rotating the SBP switch because there is no guarantee that the UPS output will be in perfect sync with the mains input when the UPS is online. By putting the UPS itself into bypass, the output from the UPS in bypass is exactly matching the mains input, so there will be no change when the SBP switch is rotated.

blackAces_apc
Commander
Commander
0 Likes
0
218

SBP5000RMI2U issue

This was originally posted on APC forums on 7/27/2010


Hi Guys

Before installation of the bypass panel is there any parameters we need to consider like the orientation of L-L or L-N, L-G from utility and UPS?
Co'z previously from my former company we counter some issue, as normal when the SBP was switch to Normal everything are doing fine but when we switch the SBP to bypass the utility breaker will tripped off and the UPS goes to Battery Mode.
No load connected to UPS and the SBP...,
Is there any issue if the out put of UPS is L-L and the Utility L-G or L-N with regards to the SBP?

Thanks