SAU1500 will not charge batteries - AC power is not passed through.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SAU1500 will not charge batteries - AC power is not passed through.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

0 Likes
7
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

SAU1500 will not charge batteries - AC power is not passed through.

Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • dead
  • no_ac_passthrough
  • sau1500
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

It_Guy wrote:
Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.
The SUA1500 is relatively simply in its AC power path. I'd check the obvious stuff first.

1. Test the outlet feeding the UPS with a known working lamp.

2. Make sure the white button on the back of your UPS didn't pop out http://www.apcmedia.com/resource/images/500/Back/53D48A24-5056-9170-D3E47E75AF003395_pr.jpg

The integral circuit breaker is connected in series with the hot and when it pops, it interrupts the input power path.
There aren't many components to go bad in the AC path. When the UPS is not on inverter, the power is directly fed through relays.

The autotransformer is transparent to the load under normal line conditions, but it has two additional taps that provides 0.88x and 1.12x of line voltage and the relays mechanically switch to one of these taps under abnormal line conditions and you would know when this is happening by the status LED on the front panel.

Because it runs fine on battery, you automatically know the transformer is fine. Since the relays appear to be making a proper transfer on the 120v side, they're like fine too.

After checking the above two check points, check the input power path. If this checks out fine, then the problem is in one of the relays or the control circuit. From there, you can transplant the relay from salvage UPSs, but if it's the board, I usually consider it a total loss.

Remove battery, charge up and save as a spare. Charge it up every 6 months. Trade the dead chassis in to TradeUPS or just get a new one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:51 AM

I am in Cordova Tn. We are a full service center and Gold Partner with APC. If you would like to give me a call at 800-365 -8816, maybe I can help. My name is Erin.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

If I am understanding correctly, your UPS will only turn on to battery power? What is the chance that its not plugged into a good power source? Can you test the current power source with a voltmeter, or perhaps plug this UPS into the same exact power outlet that your other UPS is plugged into? If you have a management card or management software with the troubled UPS, you may be able to log in and find out what is happening by reviewing the log files.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

I have tested the power with a volt meter, I remover the cover and tested the line voltage through the circuit breaker.

The software says "discharging"

There is never a online led.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:52 PM . Last Modified: ‎2024-03-26 01:50 AM

!http://i141.photobucket.com/albums/r50/DevoBill/APC_UPS_09-05-07.jpg!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

Hello,

We do not provide any info about internal components that may be able to be repaired in the our units. For out of warranty repairs, try Coastal Business Machines (888-234-9877)

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:53 PM . Last Modified: ‎2024-03-26 01:50 AM

It_Guy wrote:
Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.
The SUA1500 is relatively simply in its AC power path. I'd check the obvious stuff first.

1. Test the outlet feeding the UPS with a known working lamp.

2. Make sure the white button on the back of your UPS didn't pop out http://www.apcmedia.com/resource/images/500/Back/53D48A24-5056-9170-D3E47E75AF003395_pr.jpg

The integral circuit breaker is connected in series with the hot and when it pops, it interrupts the input power path.
There aren't many components to go bad in the AC path. When the UPS is not on inverter, the power is directly fed through relays.

The autotransformer is transparent to the load under normal line conditions, but it has two additional taps that provides 0.88x and 1.12x of line voltage and the relays mechanically switch to one of these taps under abnormal line conditions and you would know when this is happening by the status LED on the front panel.

Because it runs fine on battery, you automatically know the transformer is fine. Since the relays appear to be making a proper transfer on the 120v side, they're like fine too.

After checking the above two check points, check the input power path. If this checks out fine, then the problem is in one of the relays or the control circuit. From there, you can transplant the relay from salvage UPSs, but if it's the board, I usually consider it a total loss.

Remove battery, charge up and save as a spare. Charge it up every 6 months. Trade the dead chassis in to TradeUPS or just get a new one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore