Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

SAU1500 will not charge batteries - AC power is not passed through.

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: SAU1500 will not charge batteries - AC power is not passed through.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
It_Guy_apc
Crewman It_Guy_apc
Crewman

Posted: ‎2021-06-28 07:52 PM

0 Likes
7
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

SAU1500 will not charge batteries - AC power is not passed through.

This was originally posted on APC forums on 9/6/2007


Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • dead
  • no_ac_passthrough
  • sau1500
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KVAr_apc
Captain KVAr_apc
Captain

Posted: ‎2021-06-28 07:53 PM

0 Likes
0
284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:53 PM

This was originally posted on APC forums on 9/7/2007


It_Guy wrote:
Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.
The SUA1500 is relatively simply in its AC power path. I'd check the obvious stuff first.

1. Test the outlet feeding the UPS with a known working lamp.

2. Make sure the white button on the back of your UPS didn't pop out http://www.apcmedia.com/resource/images/500/Back/53D48A24-5056-9170-D3E47E75AF003395_pr.jpg

The integral circuit breaker is connected in series with the hot and when it pops, it interrupts the input power path.
There aren't many components to go bad in the AC path. When the UPS is not on inverter, the power is directly fed through relays.

The autotransformer is transparent to the load under normal line conditions, but it has two additional taps that provides 0.88x and 1.12x of line voltage and the relays mechanically switch to one of these taps under abnormal line conditions and you would know when this is happening by the status LED on the front panel.

Because it runs fine on battery, you automatically know the transformer is fine. Since the relays appear to be making a proper transfer on the 120v side, they're like fine too.

After checking the above two check points, check the input power path. If this checks out fine, then the problem is in one of the relays or the control circuit. From there, you can transplant the relay from salvage UPSs, but if it's the board, I usually consider it a total loss.

Remove battery, charge up and save as a spare. Charge it up every 6 months. Trade the dead chassis in to TradeUPS or just get a new one.

See Answer In Context

Reply
Share
Replies 7
It_Guy_apc
Crewman It_Guy_apc
Crewman

Posted: ‎2021-06-28 07:52 PM

0 Likes
0
284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

This was originally posted on APC forums on 9/6/2007


Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.

Reply
Share
erin128_apc
Lt. Commander erin128_apc
Lt. Commander

Posted: ‎2021-06-28 07:52 PM

0 Likes
0
284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

This was originally posted on APC forums on 9/7/2007


I am in Cordova Tn. We are a full service center and Gold Partner with APC. If you would like to give me a call at 800-365 -8816, maybe I can help. My name is Erin.

Reply
Share
dirtfoot_apc
Lt. Commander dirtfoot_apc
Lt. Commander

Posted: ‎2021-06-28 07:52 PM

0 Likes
0
284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

This was originally posted on APC forums on 9/7/2007


If I am understanding correctly, your UPS will only turn on to battery power? What is the chance that its not plugged into a good power source? Can you test the current power source with a voltmeter, or perhaps plug this UPS into the same exact power outlet that your other UPS is plugged into? If you have a management card or management software with the troubled UPS, you may be able to log in and find out what is happening by reviewing the log files.

Reply
Share
It_Guy_apc
Crewman It_Guy_apc
Crewman

Posted: ‎2021-06-28 07:52 PM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

This was originally posted on APC forums on 9/7/2007


I have tested the power with a volt meter, I remover the cover and tested the line voltage through the circuit breaker.

The software says "discharging"

There is never a online led.

Reply
Share
It_Guy_apc
Crewman It_Guy_apc
Crewman

Posted: ‎2021-06-28 07:52 PM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:52 PM

This was originally posted on APC forums on 9/7/2007


!http://i141.photobucket.com/albums/r50/DevoBill/APC_UPS_09-05-07.jpg!

Reply
Share
Sgt._Slaughter_apc
Lt. Commander Sgt._Slaughter_apc
Lt. Commander

Posted: ‎2021-06-28 07:53 PM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:53 PM

This was originally posted on APC forums on 9/7/2007


Hello,

We do not provide any info about internal components that may be able to be repaired in the our units. For out of warranty repairs, try Coastal Business Machines (888-234-9877)

Thanks.

Reply
Share
KVAr_apc
Captain KVAr_apc
Captain

Posted: ‎2021-06-28 07:53 PM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 07:53 PM

This was originally posted on APC forums on 9/7/2007


It_Guy wrote:
Hi I have an SAU1500 that will not charge old or new batteries. It beeps when you push the ON switch. I have charged the batteries in another UPS and installed them back in this UPS and then it will test the batteries and run in backup mode until the batteries are dead.

Is there a fuse or something I could check or replace?

This condition happened during a load test.
The SUA1500 is relatively simply in its AC power path. I'd check the obvious stuff first.

1. Test the outlet feeding the UPS with a known working lamp.

2. Make sure the white button on the back of your UPS didn't pop out http://www.apcmedia.com/resource/images/500/Back/53D48A24-5056-9170-D3E47E75AF003395_pr.jpg

The integral circuit breaker is connected in series with the hot and when it pops, it interrupts the input power path.
There aren't many components to go bad in the AC path. When the UPS is not on inverter, the power is directly fed through relays.

The autotransformer is transparent to the load under normal line conditions, but it has two additional taps that provides 0.88x and 1.12x of line voltage and the relays mechanically switch to one of these taps under abnormal line conditions and you would know when this is happening by the status LED on the front panel.

Because it runs fine on battery, you automatically know the transformer is fine. Since the relays appear to be making a proper transfer on the 120v side, they're like fine too.

After checking the above two check points, check the input power path. If this checks out fine, then the problem is in one of the relays or the control circuit. From there, you can transplant the relay from salvage UPSs, but if it's the board, I usually consider it a total loss.

Remove battery, charge up and save as a spare. Charge it up every 6 months. Trade the dead chassis in to TradeUPS or just get a new one.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc