Random on-line to on-battery with minimal load?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Random on-line to on-battery with minimal load?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:22 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
5
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:22 AM . Last Modified: ‎2024-03-26 10:33 PM

Random on-line to on-battery with minimal load?

My Back-UPS XS-900 has performed flawlessly for several years. Recently it began to behave strangely.

First, this behavior happens ONLY on light load (likely under 25 watts). Under my "full" load Power Chute software suggests that I'm drawing nearly 100 watts. Under these conditions all is well. 

When I turn off my computer the load goes to a minimum AND after some period of time the UPS will begin randomly switching from On-battery to On-Line. It does this 8 or 10 times and then settles back for some random period and starts again. It does this over and over.

When this first began I noticed that the batteries were long in the tooth so I replaced them. That had no impact on the problem.

A review of the Power Chute software indicates an input voltage of 103 volts. Measured voltage at the AC plug used by the UPS is 118 volts?

Thoughts appreciated. Thanks!

Rick

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

Thanks for the reply Bill. Unfortunately with the erroneous voltage reading the alarm periodically gets triggered and the UPS goes onto battery. I've seen input voltage readings (according to ACPUPSD) as high as 108 VAC and as low as 94 VAC. This happens even with a steady line voltage of 117 VAC. In addition, the MEASURED output voltage is now quite high (in excess of 130 VAC).

This UPS has served me well but I'm afraid that trusting it much longer might be risky. So I think it's time to retire the unit.

Again, thank you for the prompt reply.

Rick

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:22 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:22 AM . Last Modified: ‎2024-03-26 10:33 PM

Today my Back-UPS Pro 1000 just started experiencing nearly the same thing, although mine sits at a fairly consistent 66-75w all the time. Mine powers a FreeNAS server, so Power Chute is not available to see what the event log might show. Nobody replied to this issue here (as seems to be the case for many posts I see on here), but have you gotten any resolution to it elsewhere perhaps? It's more than a bit disturbing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

Thanks for the reply AJ. I have not resolved the problem "yet". I still think that the APC UPS  line voltage sensing circuit is the problem. It senses a voltage well below the actual line voltage and then if it makes an excursion of a few volts lower it sounds an alarm.

I took the unit out of service and I "plan" to look into the box BUT without a schematic it's a long shot.

Rick

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

Hi again AJ.

Well I have some info on MY problem. My APC Back-UPS Pro 900XS was on-line when the input voltage fell too low. That is too low according to the PowerChute software (the measured line voltage was 117 VAC.). Apparently this is a known problem. According to:

       https://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/5680/power...

The last item in this discussion explains "I talked with one of our engineers and discovered the issue is caused by the Back-UPS firmware. The issue has been addressed in later firmware releases. Unfortunately Back-UPS do not have upgradeable firmware."

WHY APC hasn't answered our questions through this forum or through the PowerChute software is unclear.

Rick

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

Hi,

Sorry you are not happy with the unit. As listed in the post you linked the issue has been corrected within the firmware. You should contact local support if you feel the unit is not working as expected. If the unit is under warranty they will assist with a replacement. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

0 Likes
0
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-26 10:33 PM

Thanks for the reply Bill. Unfortunately with the erroneous voltage reading the alarm periodically gets triggered and the UPS goes onto battery. I've seen input voltage readings (according to ACPUPSD) as high as 108 VAC and as low as 94 VAC. This happens even with a steady line voltage of 117 VAC. In addition, the MEASURED output voltage is now quite high (in excess of 130 VAC).

This UPS has served me well but I'm afraid that trusting it much longer might be risky. So I think it's time to retire the unit.

Again, thank you for the prompt reply.

Rick

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of