RS BR1500 - Reports running on battery when plugged in

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • RS BR1500 - Reports running on battery when plugged in
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

0 Likes
4
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

RS BR1500 - Reports running on battery when plugged in

I purchased an APC BACK-UPS RS BR1500 1500VA/865W UPS from Amazon 5 months ago. Last night it spontaneously powered off, and when I powered it back on, it reports that it is on battery power, even though it is plugged in. Confirmed the outlet works correctly, tried several other outlets, all to no avail. I have only the middle amber light on and it is constantly lit.

Please advise what my next step should be.


Thank you,

JT

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

I am having a similar problem and was wondering if there are any known issues with the BR1500 ? I have logged a ticket into support and I am awaiting a response. In the meantime I am trying to figure out what's gone wrong.

The unit started reporting an "Overload" condition even though there was nothing plugged-in to the unit. Now it's just "On Battery" the whole time. When I disconnect the internal battery, the unit will not turn on. Only the "Surge Only" plugs are energized (120V shown on a multimeter, but only 25V on the "Battery Backup" plugs).

After using PowerChute to try and figure out what was going on, I noticed that the input voltage was continuously changing : from ~60V to 120V or so. I have another APC unit (BN1250) which is working fine and for which the reported voltage is stable at 120V. So to ascertain that the problem was not coming from the power source, I plugged this unit in the SAME outlet as the BN1250.

The fluctuating voltage is reported on the BR1500 unit still (but not on the BN1250). I can move the unit anywhere in my home and still see the same problem.

I used to have a BR24BP plugged into it but now that the BR1500 unit is failing, it's useless.

Any ideas on what could be wrong with the BR1500 and why it's not switching to the AC power source or why it's showing a fluctuating voltage even though the source is stable ?

Thanks,
Nicolas.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

Hi Jeremy,

It would help us further diagnose the issue if you could provide the exact model number of your UPS. To give you an idea, the Back-UPS would run on battery if it has detected a power problem from the input source. Our Back-UPS checks for power problem that are present on the input source such as over/ undervoltage, frequency distortion, harmonic distortion, dirty power etc. It is like although you are getting 120V AC on your outlet, the frequency that is being fed to the UPS is not acceptable. Our UPS would then switch to on battery to protect the load.

Have you installed the PowerChute Personal Edition? This software would help you identify what kind of power problem our UPS detects.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

I am having a similar problem and was wondering if there are any known issues with the BR1500 ? I have logged a ticket into support and I am awaiting a response. In the meantime I am trying to figure out what's gone wrong.

The unit started reporting an "Overload" condition even though there was nothing plugged-in to the unit. Now it's just "On Battery" the whole time. When I disconnect the internal battery, the unit will not turn on. Only the "Surge Only" plugs are energized (120V shown on a multimeter, but only 25V on the "Battery Backup" plugs).

After using PowerChute to try and figure out what was going on, I noticed that the input voltage was continuously changing : from ~60V to 120V or so. I have another APC unit (BN1250) which is working fine and for which the reported voltage is stable at 120V. So to ascertain that the problem was not coming from the power source, I plugged this unit in the SAME outlet as the BN1250.

The fluctuating voltage is reported on the BR1500 unit still (but not on the BN1250). I can move the unit anywhere in my home and still see the same problem.

I used to have a BR24BP plugged into it but now that the BR1500 unit is failing, it's useless.

Any ideas on what could be wrong with the BR1500 and why it's not switching to the AC power source or why it's showing a fluctuating voltage even though the source is stable ?

Thanks,
Nicolas.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:04 AM . Last Modified: ‎2024-03-22 12:59 AM

I purchased an APC BACK-UPS RS BR1500 1500VA/865W UPS from Amazon 5 months ago. Last night it spontaneously powered off, and when I powered it back on, it reports that it is on battery power, even though it is plugged in. Confirmed the outlet works correctly, tried several other outlets, all to no avail. I have only the middle amber light on and it is constantly lit.

Please advise what my next step should be.


Thank you,

JT

Reply

Link copied. Please paste this link to share this article on your social media post.

eshopper
eshopper
Cadet

Posted: ‎2025-01-07 11:05 AM

0 Likes
0
197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-07 11:05 AM

Here is what I did with my situation. APC BR1500 went on battery mode when temperature suddenly dropped to the 20s. I monitored the incoming voltage via PowerChute and it reads 97-107, pretty close to the 95 minimum voltage I set.  So, I suspect low voltage was what tripped the unit into battery mode.

 

1. So, I set the voltage lower bound to 94 (the lowest it allows)

 

2. I also dropped the sensitivity to medium. It has been on High for years without issue.

 

3. I disconnected all the devices from the UPS, shut it down but let it plug in to wall while monitoring the voltage. Voltage stabilized over time (after 5 mins or so, your time may vary).

 

4. I pressed and hold the power on button for 6 seconds. It powers up and goes into self test mode and is able to get out of the battery mode in the end.

 

I also have a BR24BP (external battery pack), which I disconnected to isolate the problem. I was able to connect it back later without issue. 

 

I also tried to disconnect the wall plug and batteries on the BR1500 and tried the 5 seconds power button hold to reset it. (My understanding is it drains the capacitors which resets its state) It didn't fix the battery power stuck issue.

 

This model probably doesn't have a voltage regulator/filter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of