Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

RS-900 No Power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: RS-900 No Power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:35 AM

0 Likes
3
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:41 PM . Last Modified: ‎2024-03-21 02:35 AM

RS-900 No Power

Hello All,

I have about 20 RS-900's that I have had in storage for well over a year. I recycle electronics and these units were given to me in an unknown condition. I am unable to get any activity on the units. I dont hear any noise, see any lights, or get any power from battery backup side of outlets. The surge only outlets provide ample power. I have plugged each one of these in following cold start protocol, and after reviewing the manual and reading many other forum posts I am at a loss. I have read that if the batteries are completely drained you wont get any power but thats hard to believe. I would like to resurrect these if possible rather than scrap them. Any ideas? First few of serials 5B0741U.

Thanks~!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

lifecycles wrote:
Thanks for the recommendation. I received a new battery. The battery is charged. When I plug the battery into the units the green light comes on.
When you did this, was the unit on or off? If it was off, did you mean that the unit turned on by itself?
lifecycles wrote:
The UPS is not plugged into the wall nor is there any load plugged into it. After a few seconds the red overload light appears and stays steady.
Though the unit was not plugged in on any power source, what was the state of the UPS? Did it went on overload while the unit was off or was it running on battery and then it went to overload?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:35 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:35 AM

To start with, it would be helpful if you could grab a fresh new battery for the UPS. If you could get one, we can use that to test all 20 UPSs that you have. With regards to the serial the 3rd digit up to the 6th would tell us the year and the week that it was manufactured. On the S/N that you have given us, we can tell that it was made on the 41st week of 2007. Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

Thanks for the recommendation. I received a new battery. The battery is charged. When I plug the battery into the units the green light comes on. The UPS is not plugged into the wall nor is there any load plugged into it. After a few seconds the red overload light appears and stays steady. This is consistent across all units. Any thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:42 PM . Last Modified: ‎2024-03-21 02:34 AM

lifecycles wrote:
Thanks for the recommendation. I received a new battery. The battery is charged. When I plug the battery into the units the green light comes on.
When you did this, was the unit on or off? If it was off, did you mean that the unit turned on by itself?
lifecycles wrote:
The UPS is not plugged into the wall nor is there any load plugged into it. After a few seconds the red overload light appears and stays steady.
Though the unit was not plugged in on any power source, what was the state of the UPS? Did it went on overload while the unit was off or was it running on battery and then it went to overload?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore