New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Questions about UPS's.
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-2211:31 PM
Questions about UPS's.
Hello, I run a few servers for game servers, web servers, file servers, databases, etc from my home. Ive had these older APC 1500va units for going on 8 years and ive went through 4 sets of SLA batteries in them. Sick of doing this i looked into LifePO4 batteries as replacements to just shove into the APC UPS's.
Ive watched many videos, guides, articles, etc. On how they work no different from a SLA battery in the unit, and they simulate the same voltage as a SLA battery in the UPS.
So i bought a new APC unit and 2 new LifePO4 12v 10AH batteries to try out. My results were not what i expected. 24v @ 10AH should give me 240wh which should run a 35w load for 6+ hours. Battery manufacturer also confirmed this is correct. But that 35w load only got 1 hour and 40 mins runtime...
I recharged for 48 hours and tried again, got 2 hours this time. Still far off from what i could be getting. So i bought a different brand of batteries to test to see if it was the battery itself. Same results. Both brands of batteries were only charged up to 13.25v or 26.5v for the pack in each UPS. The battery is supposed to be charged up to 14.8v, just like a SLA battery would. But both units aren't doing that...
Whats going on? Is there a fix to this? Or is there a different brand/model of UPS i can buy that has better support for lithium batteries then these? Im not looking to spend thousands of dollars, I don't have a rack, just a shelf i put these on. Im just using consumer grade UPS's. APC's "Lithium" units are massive rack mounted units that cost $1500 for the same output as the $200 unit i have now.
APC BR1500MS2 are the UPS's im using. Im using MightyMax and ECO-Worthy LifePO4 12v 10AH batteries.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-2808:12 AM
I have read your post twice now and I'm confused, but I'll give it a shot.
"Whats going on" - The firmware for the BackUPS is simply not designed to support the advanced functionality of the Li batteries.
"Is there a fix to this" - Yes, you could purchase a device that is specifically designed to properly support the functionality of Li batteries.
"Is there another brand" - Yes, E**t*n, for example, makes a P5x series. I'm sure there are others.
"I'm not looking to spend thousands" - Well, then you won't be buying Li products for quite a while. The aforementioned goes between $1250 and $1500.
Long before Schneider Electric took over, APC had a "3-5-7" approach for UPS devices. Batteries will usually last from 3 to 5 years, so they wanted to make sure you purchased an extended warranty. If the battery went during initial warranty, you were covered with a free replacement. If it went during the extension, you were also covered. At 7 years they wanted you to use the Trade-UPS program to replace the device with a newer one, offering a slight discount. That program eliminated BackUPS devices earlier this year - only SmartUPS are eligible.
I've been reselling APC UPSs for over a decade and my clients have never had to purchase a replacement battery outright.
The stated goals of Li batteries are longevity and the elimination of replacement batteries over the life of the unit. The technology - at least for now - is expensive.
Bottom line: I don't think you are going to achieve what you want from an ad-hoc solution, especially using consumer-based products.