I find that Back-UPS ES 500 doesn't correct any noise in the range 10-15 V when the input voltage is less than 205 V and around greater than 180 V (i found this using APC PowerChute application),but when the voltage is above 205 V UPS keeps on correcting noise either through AVR or using battery power.
My question is that, is electrical noise below 205 V normal or this is a bug in hardware ?
*************EDIT*******************
It was a bug in Back-UPS ES 500,APC PowerChute application shows incorrect information regarding the status of UPS.
I have shown here a snap shot of current status of UPS,in it its showing 'Your battery backup is operating normally' @ input 156 V , I have then tested the output voltage using multimeter and found out that its 220 V.
Message was edited by: prince213
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:03 AM
I find that Back-UPS ES 500 doesn't correct any noise in the range 10-15 V when the input voltage is less than 205 V and around greater than 180 V (i found this using APC PowerChute application),but when the voltage is above 205 V UPS keeps on correcting noise either through AVR or using battery power.
My question is that, is electrical noise below 205 V normal or this is a bug in hardware ?
*************EDIT*******************
It was a bug in Back-UPS ES 500,APC PowerChute application shows incorrect information regarding the status of UPS.
I have shown here a snap shot of current status of UPS,in it its showing 'Your battery backup is operating normally' @ input 156 V , I have then tested the output voltage using multimeter and found out that its 220 V.
Message was edited by: prince213
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-26 12:03 AM
I find that Back-UPS ES 500 doesn't correct any noise in the range 10-15 V when the input voltage is less than 205 V and around greater than 180 V (i found this using APC PowerChute application),but when the voltage is above 205 V UPS keeps on correcting noise either through AVR or using battery power.
My question is that, is electrical noise below 205 V normal or this is a bug in hardware ?
*************EDIT*******************
It was a bug in Back-UPS ES 500,APC PowerChute application shows incorrect information regarding the status of UPS.
I have shown here a snap shot of current status of UPS,in it its showing 'Your battery backup is operating normally' @ input 156 V , I have then tested the output voltage using multimeter and found out that its 220 V.
Message was edited by: prince213
Link copied. Please paste this link to share this article on your social media post.