Problems with my UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Problems with my UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
106
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
7
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-27 12:04 AM

Problems with my UPS

Hello everyone!

Even before i state my problem i would like you to know that im not a tech savvy guy and know very little about hardware. with that i would like to share with you guys my problem

I had a UPS(not APC) which i have been using for almost a year. About 3 months back my UPS started failing me. That is whenever there was a power failure my UPS wouldn't switch to backup and my computer would shutdown. I thought that my UPS is broke and as a typical novice i immediately decided to buy another UPS. After lot of asking around i found out that APC has a good range of UPS. So i went about and bought APC Back-UPS 600, 230V without auto shutdown software. I started using it immediately and i was thoroughly satisfied with it. Until a few days back i once again experienced a power failure, and mind you this isn't the first power failure my new UPS has faced. But this time something unusual happened. My system was restarting... i was confused. Unlike my last UPS which totally shut down. this one was restarting. I brushed it as a an accident and i was actually convinced... as after the incident my UPS responded well to upcoming power failures. But then again the same thing happened. My initial guess is it fails occasionally. To simulate a power failure i cut the main power to my system. How many ever times i tried this my UPS back up always kicked in. Only when a real power failure occurred this thing happens that too not all the time. I'm on an edge now as i will never know when the power is going to go off and when my UPS is going to fail and making me lose progress.

So i ask for help to determine my problem and how to fix this. If you need any other information other that the one I've provided please ask me and I'll do my best to provide it. Thank you in advance

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

You can reach India APC support on 18004194272

Regards,

Vinay

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

Hi Tarum , can you send a photo of your connection between your pc and the ups? before the restart your pc shows some message or it restarts inmediately?   , try changing the cable between ups and pc , maybe it is bad. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

Ty for the reply and sorry to the delay...

 So i have my moniter, CPU connection and sound system connected to a spike suppressor and the spike suppressor is connected to my ups.

And no I don't get any message during restart only the 'run windows normally' and 'safe mode' options.

Hope this helps

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

Hi Tarun,

This issue has been outlined in the below Kbase. Hope this answers your query on the computer reboot issue.

Link: http://www.apc.com/us/en/faqs/index?page=content&id=FA158852

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

So in short i need to replace my surge protector with a power distribution unit? if so could you please recommend one? Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

You are correct. you can go for a basic PDU or connect all the loads directly on the ups outlets. Can I know which country the UPS is located? based on that I can provide you the contact information for the PDU recommendation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

On 10/10/2017 5:38 PM, Vinay said:

You are correct. you can go for a basic PDU or connect all the loads directly on the ups outlets. Can I know which country the UPS is located? based on that I can provide you the contact information for the PDU recommendation.

I live in India...and thank you very much!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-27 12:04 AM

You can reach India APC support on 18004194272

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore