Powerchute says RS 800 is overloaded, no led though

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Powerchute says RS 800 is overloaded, no led though
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

0 Likes
9
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:30 AM

Powerchute says RS 800 is overloaded, no led though

The last few weeks I have 2 RS 800's that are giving me fits. The set ups are nearly identical, so I'll focus on one, but the problems are identical with both. We have one small server plugged into each of them, about 300W according to the server manufacturer. APC replaced the original two units, but I'm getting the same symptoms on the new units. I let the units charge over a full weekend. I have been exchanging emails with APC tech support, but my questions aren't answered very well.

Powerchute PE says that there is an overload condition, that the unit is supplying 216W. The front panel overload led is NOT lit. I've attached a pdf screen snap of the overload message.

I don't believe the unit is or should be overloaded; if it truly is, why isn't the front panel led lit?

What am I missing here?

Thanks,
Chuck

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

The last few weeks I have 2 RS 800's that are giving me fits. The set ups are nearly identical, so I'll focus on one, but the problems are identical with both. We have one small server plugged into each of them, about 300W according to the server manufacturer. APC replaced the original two units, but I'm getting the same symptoms on the new units. I let the units charge over a full weekend. I have been exchanging emails with APC tech support, but my questions aren't answered very well.

Powerchute PE says that there is an overload condition, that the unit is supplying 216W. The front panel overload led is NOT lit. I've attached a pdf screen snap of the overload message.

I don't believe the unit is or should be overloaded; if it truly is, why isn't the front panel led lit?

What am I missing here?

Thanks,
Chuck

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Two instances - one OS is Windows Server 2000 SP4, the other is Server 2003 SP1.

Based on the question, I looked a little bit at the Power Options in Control Panel, but didn't see anything obvious there that could be/should be changed. How does the OS talk to Powerchute or the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Chuck,

If PowerChute is installed, you cannot configure or control anything via Control Panel. However, if you remove PowerChute, you lose the graphical interface, and there is a bare-bones base setup for low battery shudown.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

I'm curious, does this overload happen as soon as you install the software, or only after a self-test / on battery instance?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Good question. This has been an ongoing situation and it was first discovered a few weeks ago during a casual inspection, so I don't remember exactly what the circumstances and sequence were.

When I replaced the UPS', I ran self-test via Powerchute very shortly after the servers were up. The overload condition as reported by Powerchute happens as soon as self-test completes. (FWIW, the overload condition is cleared during the first part of the self-test.)

Edited to add: (I thought I'd put this information in earlier, sorry.) Dell's configurator tool says that these servers should draw 301.7W.

Thanks,

Chuck

Message was edited by: Chuckhubbert

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Hello Chuck,

The Dell configurator holds true with APC's selector, maxing out at 354W/506VA, therefore should be enough to be supported by the UPS. What operating system is included in this package? It's possible that the UPS is sensing a near overload and is not reporting it, but the software is sensing the at or near overload and reporting it as an FYI.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Came in this (Monday) morning to find the units alarming with the Overload led flashing and the servers powered down. I went ahead and took the UPS' out of service, since they aren't helping in any fashion right now, apparently.

I still have lots of questions... These servers should not be overloading the UPS', but it appears that they are. I don't have any way to measure current.
Anybody have any guesses as to why that might be happening?

What triggers the overload condition in Powerchute? And does anyone know what that threshold should be for the RS 800's?

I have put one of the UPS back into service on my workstation/PC and it seems to be working fine, drawing about 75W.

Message was edited by: Chuckhubbert

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Hello,

For starters it should be mentioned (if it hadn't been prior), that Back-UPS are not desigend for server use. They are Home/PC UPS systems. Smart-UPS, due to their intelligence, and output of a pure sine wave on battery, are more geared towards network and servers. Secondly, it could be that there was some type of load fluctuation if the server was scheduled to do a backup of files, or any type of service that may have required an increased power draw.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

Hello,

What is exactly connected to the UPS Battery Backup outlets?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

0 Likes
0
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:16 PM . Last Modified: ‎2024-03-26 01:29 AM

The last few weeks I have 2 RS 800's that are giving me fits. The set ups are nearly identical, so I'll focus on one, but the problems are identical with both. We have one small server plugged into each of them, about 300W according to the server manufacturer. APC replaced the original two units, but I'm getting the same symptoms on the new units. I let the units charge over a full weekend. I have been exchanging emails with APC tech support, but my questions aren't answered very well.

Powerchute PE says that there is an overload condition, that the unit is supplying 216W. The front panel overload led is NOT lit. I've attached a pdf screen snap of the overload message.

I don't believe the unit is or should be overloaded; if it truly is, why isn't the front panel led lit?

What am I missing here?

Thanks,
Chuck

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of